    Metallic conduit body between PVC runs.

    Guys installed metallic conduit bodies between runs of PVC. Any solution to bond these other than drill and nut and bolt a lug to them? No clue why they didnt install EMT.

  2. #2
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,102
    Quote Originally Posted by Transportation Guy View Post
    Guys installed metallic conduit bodies between runs of PVC. Any solution to bond these other than drill and nut and bolt a lug to them? No clue why they didnt install EMT.
    If you drill the body to install a lug, you end up with an issue of voiding the product listing. Perhaps a bonding U-bolt or bonding strap around the circular hubs might work, in which case you'd need a #6 bonding jumper running to a point where you can connect it to the EGC system.

  3. #3
    Join Date
    Jan 2009
    Location
    Williamsburg,VA
    Posts
    112
    Thanks. Changing it all to EMT