Results 1 to 3 of 3
Thread: Metallic conduit body between PVC runs.
  1. #1
    Join Date
    Jan 2009
    Williamsburg,VA
    Posts
    112
    Guys installed metallic conduit bodies between runs of PVC. Any solution to bond these other than drill and nut and bolt a lug to them? No clue why they didnt install EMT.
  2. #2
    Join Date
    May 2013
    Massachusetts
    Posts
    2,293
    Quote Originally Posted by Transportation Guy View Post
    If you drill the body to install a lug, you end up with an issue of voiding the product listing. Perhaps a bonding U-bolt or bonding strap around the circular hubs might work, in which case you'd need a #6 bonding jumper running to a point where you can connect it to the EGC system.
  3. #3
    Join Date
    Jan 2009
    Williamsburg,VA
    Posts
    112
    Thanks. Changing it all to EMT
Posting Permissions
  • You may not post replies
  • You may not edit your posts