    Delta- Delta transformer

    I have a 480v pri 240v sec Delta-Delta transformer. I'm questioning how to bond it. The transformer diagram has nothing on Grounding the B phase (x2). But I'm 90% sure that is what I need to do. Before I do this I want to be 100% sure. Any help would be grateful

  2. #2
    Join Date
    May 2017
    Location
    St Louis
    Posts
    3
    Quote Originally Posted by EL Schulte View Post
    I have a 480v pri 240v sec Delta-Delta transformer. I'm questioning how to bond it. The transformer diagram has nothing on Grounding the B phase (x2). But I'm 90% sure that is what I need to do. Before I do this I want to be 100% sure. Any help would be grateful
    Will the transformer Name plate have a Grounded B phase secondary diagram on it if it is capable of being grounded?

  3. #3
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    17,026
    Quote Originally Posted by EL Schulte View Post
    Will the transformer Name plate have a Grounded B phase secondary diagram on it if it is capable of being grounded?
    Probably not.

    Sent from my XT1585 using Tapatalk

  4. #4
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,034
    I only have been around one corner grounded system, but as far as what the NEC says you pick one phase and ground it, B phase is customary but I don't think it's required. After that treat the grounded phase just like a neutral and follow 250.30 and 200.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  5. #5
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    6,280
    You don't actually HAVE TO ground one phase, you DO have to do that OR you must add ground fault monitoring and protection to the secondary side; one or the other. So the transformer nameplate diagram is not likely to show that, it's an installation decision on your part. It's a lot less expensive however to just use a corner grounded secondary and yes, B phase is the conventionally accepted one to ground, but it's not dictated.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  6. #6
    Join Date
    May 2017
    Location
    St Louis
    Posts
    3
    Thank you this helps. One more question. This transformer will be supplying a panel for 3 phase 240v equipment only. I can use 3 pole breakers right.

  7. #7
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    31,289
    Quote Originally Posted by EL Schulte View Post
    Thank you this helps. One more question. This transformer will be supplying a panel for 3 phase 240v equipment only. I can use 3 pole breakers right.
    As long as the breakers are 240 volt and not 120/240 volt rated, but most 3 pole are not rated 120/240 AFAIK.

    The transformer will not care which leg you ground, as long as there is only one leg grounded, more then one leg grounded is short circuit.

    Make sure panel is rated for grounded phase system as well though. If so it may say "B" must be the grounded phase.