Page 2 of 3 FirstFirst 123 LastLast
Results 11 to 20 of 26
Thread: Sand Gas Line to bare metal
  1. #11
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    35,668
    Quote Originally Posted by augie47 View Post
    Post #7 (after yours) is part of the key. We finally get the point across that the EGC can serve as the bond then the CSST rules come into play and we have to use that word "except".
    My experience when there are variables, such as here or one vs two rods, etc., some contractors just tell there men to take the cautious road rather than have to go back.
    IMO inspecting bonding of CSST isn't the job of an EI, should be whoever inspects the gas piping, special bonding rules of such piping only apply to one series of product and not to gas piping in general.
    Haven't been asked to bond any for some time now but considering telling anyone that does ask to pound sand, if anything install an intersystem bonding terminal if one isn't present and tell them it is there for others to use to connect to the electrical grounding system. Special bonding of such piping is one task of installing the piping and I am not a gas line installer.
  2. #12
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    4,089
    Yes I agree that CSST may require bonding per the manufacturer, but I also agree with Kwired that in that case, its not my job. .
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  3. #13
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by electrofelon View Post
    ... its not my job. .
    So you wouldn't do it even if you get paid to do it?
    I will have achieved my life's goal if I die with a smile on my face.
  4. #14
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    35,668
    Quote Originally Posted by Smart $ View Post
    What is my liability and is it worth it? I am not a gas pipe fitter, my insurance assumes I don't do gas pipe fitting. Installing this bonding conductor(s) is a task of installing certain types of gas piping and is not "electrical installations".
    I have done electrical work at bulk fuel plants and seen bonding jumpers installed between fuel piping, tanks, and other equipment by the fuel guys. why is this CSST any different. They need to put in whatever is necessary to protect their equipment, I only need to install a GES for the electrical system and EGC's with my branch circuits and feeders, I am required to bond to metal piping systems, but gas piping is allowed to be bonded by "my code" by the EGC of the circuit(s) most likely to energize the piping - most cases the EGC to a furnace supplied by the piping.
  5. #15
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by kwired View Post
    What is my liability and is it worth it?...
    Here's an article about whose job it is.
    http://ecmweb.com/bonding-amp-ground...el-tubing-csst
  6. #16
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    35,668
    ECM doesn't tell me what my job is
    Said this before even looking at the link BTW.
  7. #17
    Join Date
    Jun 2004
    Posts
    4,089
    Nazi soldiers got paid to commit genocide. Sometimes its about principles and what's right not money
  8. #18
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    You two seem quite adamant about not doing it. I do not believe you have a legitimate reason. Either way, no skin off my baseballs. It's just that you two make it sound as though no electrician should touch CSST bonding. Doing it or not is a matter of choice... and the right to make that choice.
  9. #19
    Join Date
    Jun 2003
    Hawthorne, New York NEC: 2014
    Posts
    3,466
    ... install an intersystem bonding terminal if one isn't present and tell them it is there for others to use to connect to the electrical grounding system. Special bonding of such piping is one task of installing the piping and I am not a gas line installer.
    I'm surprised someone doesn't suggest that it is the ECs responsibility to provide the ground bond for telephone, cable and satellite too.
    -Hal
  10. #20
    Join Date
    Feb 2003
    Illinois
    Posts
    23,464
    There is nothing in the NEC that requires bonding for the CSST other than the EGC that serves the equipment connected to the CSST. You have to go to other codes or manufacturer's instructions to get the CSST bonding. There were a number of attempts to get that bonding in the NEC but were rejected by CMP5 because there is no credible technical substantiation to support those bonding requirements. The CSST people took an end run and got rules in NFPA 54 to require that bonding, but not sure how many places actually adopt 54 as an enforceable document.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
Posting Permissions
  • You may not post replies
  • You may not edit your posts