Page 3 of 3 FirstFirst 123
Results 21 to 26 of 26
Thread: Sand Gas Line to bare metal
  1. #21
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by don_resqcapt19 View Post
    ... The CSST people took an end run and got rules in NFPA 54 to require that bonding, but not sure how many places actually adopt 54 as an enforceable document.
    But it's enforceable if the instructions say it has to be bonded other than by the connected electrical equipment, right?
    I will have achieved my life's goal if I die with a smile on my face.
  2. #22
    Join Date
    Feb 2003
    Illinois
    Posts
    23,352
    Quote Originally Posted by Smart $ View Post
    Not enforceable under the NEC and not required of the EC.
    The responsibility is on the contractor who installed the product. If that contractor wants to pay me to do it, fine.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  3. #23
    Join Date
    Mar 2008
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,614
    Quote Originally Posted by hbiss View Post
    I'm surprised someone doesn't suggest that it is the ECs responsibility to provide the ground bond for telephone, cable and satellite too.
    -Hal
    It is here. For several years now, every new service installed, and every service upgrade done has to have an intersystem bonding connector.
    Cheers and Stay Safe,
    Marky the Sparky
  4. #24
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,704
    Quote Originally Posted by K8MHZ View Post
    That is not bonding the phone, satellite, etc. that is leaving a designated location for those installers to make their connection to the electrical system grounding network.
  5. #25
    Join Date
    Mar 2008
    Posts
    9,614
    Quote Originally Posted by kwired View Post
    I didn't say it was bonding. I was responding to 'providing a ground bond', which I took to be an IBC, which is more than a location, it is an actual connector.
    Marky the Sparky
  6. #26
    Join Date
    Jun 2003
    Hawthorne, New York NEC: 2014
    Posts
    3,330
    And in my experience cable installers do whatever they are told which does not include connecting to any IBC.
    I have two drops on my house. One is connected to a ground strap on the conduit above the meter pan. The other ground block, mounted right below the first got connected to the GEC going to the ground rods. When I asked the cable guy why didn't he just loop one ground from one ground block to the other, he said there is a reason he does things that way. Ok then...