Before adoption of 2014 NEC this was not generally a requirement to use GFCI on a disposer, and still is not if it is not cord and plug connected with a 15 or 20 amp 120 volt receptacle. Local rules could vary.

2014 clarified that they wanted "within 6 feet of outside edge of a sink" to include kitchen sinks. Though they did not specifically mention receptacles in a cabinet within that 6 feet many interpret it to include those which would mean a typical cord and plug connected disposer would normally need GFCI protection.
 

E16

Member
Location
Iowa
Occupation
Electrical Contractor
Before adoption of 2014 NEC this was not generally a requirement to use GFCI on a disposer, and still is not if it is not cord and plug connected with a 15 or 20 amp 120 volt receptacle. Local rules could vary.

2014 clarified that they wanted "within 6 feet of outside edge of a sink" to include kitchen sinks. Though they did not specifically mention receptacles in a cabinet within that 6 feet many interpret it to include those which would mean a typical cord and plug connected disposer would normally need GFCI protection.

:thumbsup: May also want to ask your AHJ if under the cabinet is a "readily accesiable location" if you plan on installing a GFI under there!!
 