    In NEC 310.10(H)5, "Sectioned" equipment bonding reads differently than just equipment bonding. Can someone clear this up for me? What is Sectioned equipment? and the different application of Table 250.122 if Sectioned Equipment?
  2. #2
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    9,134
    I can't find 310.10 (H)5.
    If you go and decide to dance with a gorilla the dance ain't over till the gorilla decides it's over.
  3. #3
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Some multiconductor cables, usually in the larger sizes, will put in three EGC's to reduce the total cross-sectional area of the cable. The combined cross-sectional area of these three EGC's is equivalent to or exceeds the standard 250.122 EGC, i.e. its cross-sectional area.
    I will have achieved my life's goal if I die with a smile on my face.
  4. #4
    Join Date
    Feb 2008
    Texas
    Posts
    877
    Quote Originally Posted by ActionDave View Post
    Page 70-146 NEC-2017
    Equipment Grounding Conductors: Where parallel equipment grounding conductors are use...
  5. #5
    Join Date
    Oct 2007
    Iowa
    Posts
    6
    Quote Originally Posted by Smart $ View Post
    Thanks, that makes sense . I got hung up on "Sectioned" Equipment.
  6. #6
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,365
    Quote Originally Posted by jtp View Post
    As Smart stated it's a code permissible way to get several EGC's to make one larger one. Normally paralleling of smaller EGC's to make a larger one is not permitted.