    Bonding an gas meter

    Is grounding an gas meter as simple as installing a cold waterclamp at gas meter and then running a #6 bare and hitting the system GEC irreversibly?

  2. #2
    Join Date
    Jul 2016
    Location
    VT
    Posts
    18
    250.52 (B) (1) prohibits grounding the underground gas piping as GEC.

    However 250.104 (B) tells you the requirements needed to bond the interior gas piping. Usually if the gas appliance has a plug on it, you meet the requirements.

    To help clarify how it makes any difference. Apparently there is no continuity on the inlet and outlet of the gas meter.

  3. #3
    Join Date
    May 2011
    Posts
    3,624
    Bond on the customer's side of the gas meter. Technically I don't think it requires an irreversible splice because it is not part of the grounding electrode system.

  4. #4
    Join Date
    Jun 2015
    Location
    texas
    Posts
    1,430
    Quote Originally Posted by ArcLazerbeam View Post

    To help clarify how it makes any difference. Apparently there is no continuity on the inlet and outlet of the gas meter.

    A dielectric fitting is installed by utilities to prevent problems with their cathodic protection system on their pipes/turning their pipes into another ground.

    Gas companies will quickly remove any clamp they see on their side.

    Quote Originally Posted by jaggedben View Post
    Bond on the customer's side of the gas meter. Technically I don't think it requires an irreversible splice because it is not part of the grounding electrode system.
    Yeah if you have a black iron pipe installation, its not needed- the egc on the appliance takes care of bonding.

    If the op has csst, then he could bond on the rigid at meter, and that will suffice for the required bonding of the csst.

    And no, irreversibility not needed.

    To the OP: just make sure your clamp is listed for UL 467- Ericos are great and would work.
    Last edited by user 100; 05-14-17 at 08:51 PM. Reason: added thought

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    32,135
    Quote Originally Posted by jaggedben View Post
    Bond on the customer's side of the gas meter. Technically I don't think it requires an irreversible splice because it is not part of the grounding electrode system.
    only the grounding electrode conductor requires irreversible splices, this would be a bonding jumper.

  6. #6
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,128
    Quote Originally Posted by kwired View Post
    only the grounding electrode conductor requires irreversible splices, this would be a bonding jumper.
    I agree, as long as you don't cut the GEC to connect to it. Split bolt works well for these connections.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #7
    Join Date
    May 2011
    Posts
    3,624
    Quote Originally Posted by kwired View Post
    only the grounding electrode conductor requires irreversible splices, this would be a bonding jumper.
    There's a couple inspectors around here who need you to come tell them that.

  8. #8
    Join Date
    May 2017
    Location
    Kernersville NC USA
    Posts
    6

    Thanks for the info

    Around here, it's not the AHJ that are asking for it, it's the home inspectors that are asking for it on their reports. So basically, we have been doing it right except we can use a split bolt instead of a irreversible. Thanks for all the replies.