Page 2 of 2 FirstFirst 12
Results 11 to 16 of 16
Thread: IEEE std Voltage Drop
  1. #11
    Join Date
    Jan 2014
    New Jersey
    Posts
    5
    I got it! Thanks a lot
    Quote Originally Posted by dkidd View Post
    Definition from Article 100
    Outlet. A point on the wiring system at which current is
    taken to supply utilization equipment.
    Don't confuse outlet with receptacle.
  2. #12
    Join Date
    Dec 2008
    Posts
    482
    Quote Originally Posted by schicco View Post
    Julius
    Just want to check again
    What numbers did you use for the cos(theta) and sin(theta)
    Thanks a lot
    Steve
    The angle theta has to be acos(0.8).I did now the same calculation on the other computer and the VD is close to yours indeed : 1.94943 accurate and 1.948536 approximate. Since I was 100 miles away I don't know what happened. I am sorry.
  3. #13
    Join Date
    Dec 2010
    Posts
    1,353
    Julius
    Thanks a lot
    Steve
    Correction to earlier post
    Theta is 36.86989765
    Cos(theta) is .8.
    Sin(theta) is .6
    The more they overthink the plumbing, the easier it is to stop up the drain
  4. #14
    Join Date
    Apr 2013
    New York
    Posts
    35
    Thanks a lot
    Quote Originally Posted by Julius Right View Post
  5. #15
    Join Date
    Apr 2013
    New York
    Posts
    35
    Thanks!
    Cos(theta) is .8.
    Sin(theta) is .6
  6. #16
    Join Date
    Dec 2008
    Posts
    482
    NEC 2014 art. 695.7 Voltage Drop. A) Starting 15% start. B) Running not more than 5% voltage drop from rated motor voltage at 115% load.
Posting Permissions
  • You may not post replies