Page 1 of 2 12 LastLast
Results 1 to 10 of 16
Thread: IEEE std Voltage Drop
  1. #1
    Join Date
    Apr 2013
    New York
    Posts
    35
    I have been trying to calculate the voltage drop using the IEEE std.141
    Vd = es + IRcos(theta) + IX sin(theta) + sqrt(es^2 - (IXcos(theta) - IRsin(theta))^2)
    Inputs:
    Number of conductors: Single
    Conductor size: 1/0
    Power factor: 80%
    Load Current(Amps) 91
    System voltage: 480
    Length of Run (feet) 460
    Conduit: EMT
    I am coming up with 1.62% Voltage Drop
    Am I correct?
    Using the simplified formula V = I Rcos(theta) + I Xsin(theta) I get 1.95% Voltage Drop
    Don't know which one is correct.
    Thanks a lot
  2. #2
    Join Date
    Dec 2008
    Posts
    482
    Quote Originally Posted by schicco View Post
    Inputs:
    Conductor size: 1/0
    Power factor: 80%
    System voltage: 480
    Conduit: EMT
    Am I correct?
    Thanks a lot
    At first the actual voltage drop formula is:
    Vd = es + IRcos(theta) + IX sin(theta) - sqrt(es^2 - (IXcos(theta) - IRsin(theta))^2)
    and the result is 1.9247% and from the approximate formula is 1.9233%.
    The R=0.12 ohm/1000 ft and X=0.055 ohm/1000ft from NEC Table 9 for steel conduit.
  3. #3
    Join Date
    Apr 2013
    New York
    Posts
    35
    Julius
    Thanks a lot, I see where I was going wrong. Now I am getting your numbers.
    Again thanks
    Steve
    Quote Originally Posted by Julius Right View Post
  4. #4
    Join Date
    Apr 2013
    New York
    Posts
    35
    Julius
    Just want to check again
    What numbers did you use for the cos(theta) and sin(theta)
    Thanks a lot
    Steve
  5. #5
    Join Date
    Dec 2010
    Posts
    1,353
    Julius
    Thanks a lot
    Steve
    Theta is .8. Cos theta is 0.99990252400930421155123810793869. Sin theta is 0.01396218033914527162191138769678 (roughly )
    The more they overthink the plumbing, the easier it is to stop up the drain
  6. #6
    Join Date
    Apr 2013
    New York
    Posts
    35
    Thanks a lot
    Quote Originally Posted by dkidd View Post
  7. #7
    Join Date
    Apr 2013
    New York
    Posts
    35
    Since I am feeding a fire pump motor; I should then multiply by 1.73 to get the Line to Line?
    Then it would mean I have gone way over 3% voltage drop, right?
    The 2%(feeder)+3%(branch)=5%vd applies?
    Not sure if Fire Pump falls under branch or feeder (definition of branch is wiring that comes after the final protection device)
    Thanks
  8. #8
    Join Date
    Dec 2010
    Posts
    1,353
    Yes
    Thanks
    Codes limit the running voltage drop to 5%, and starting to 15%.
  9. #9
    Join Date
    Jan 2014
    New Jersey
    Posts
    5
    What confuses me about the code definition of branch ckt ("the conductors between the branch circuit final overcurrent device protecting the circuit and the outlets") is;
    Why does it only mention outlets?
    If I am going to hard wire a motor or heating, it cannot be branch?
    From the same panel you can have an OCPD feeding outlets and another OCPD feeding a motor. Are they all not branch ckts?
    Thanks
    Andy
    Yes
    Attached Images Attached Images
  10. #10
    Join Date
    Dec 2010
    Posts
    1,353
    Quote Originally Posted by aprice44 View Post
    Thanks
    Andy
    Definition from Article 100
    Outlet. A point on the wiring system at which current is
    taken to supply utilization equipment.
    Don't confuse outlet with receptacle.
Posting Permissions
  • You may not post replies
  • You may not edit your posts