Results 1 to 8 of 8
Thread: single phase 120/240 generator on 120/208 three phase system
  1. #1
    Join Date
    Jun 2004
    Cherry Valley NY, Seattle, WA
    Posts
    3,299
    So can it be done? Say one needs a generator with auto transfer for some small line to neutral loads (or even L-L if the loads are ok with either 208 or 240). I dont see any issue from an electrical theory standpoint, but the hangup I come up with is the transfer switch accepting different voltages. Do any have this capability? There is a pretty big price jump going up to three phase genny and transfer switch.
    Ethan Brush - East West Electric. NY, WA. MA
    "You can't generalize"
  2. #2
    Join Date
    Aug 2006
    Miami Fla.
    Posts
    7,380
    The 3Ø ATS will likely see 'phase loss' on genny and fail to transfer.
  3. #3
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Might work if you set up the target loads on a 120/208 1Ø 3W panelboard and put the ATS between the 3Ø source and this panelboard.
    I will have achieved my life's goal if I die with a smile on my face.
  4. #4
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    33,684
    Quote Originally Posted by chris kennedy View Post
    If you did this you would likely have "select loads" and would have a single phase feeder supplying them from "normal power" Main issue would be if the line loss monitoring will be ok with 208 normal vs 240 standby power. I'm guessing many do not even monitor standby voltage though, if so this might not be a problem at all, as long as you can adjust the single phase transfer switch to accept the 208 nominal as an acceptable normal input voltage.
  5. #5
    Join Date
    Jun 2004
    Posts
    3,299
    Quote Originally Posted by Smart $ View Post
    Yes, that is the hypothetical plan. I'm going to dig thru some transfer switch literature and see what the parameters are for the accepted utility voltage.
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    33,684
    If you had 120 volt voltage monitoring on each line to neutral the unit won't care if it is 208 or 240 line to line. Don't know what is common to see for voltage monitoring on such units though.
  7. #7
    Join Date
    Jun 2004
    Posts
    3,299
    Quote Originally Posted by kwired View Post
    Just taking a quick look at the generac RTS line:
    "utility voltage drop out - <60%"
    "utility voltage pick up - >80%"
    So that would work with 208 if that means what I think it means. I would want their blessing before trying it though.
  8. #8
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    Quote Originally Posted by electrofelon View Post
    Yeah, I'd want their blessing too. Had a brief glimpse at the general spec's and none are stated up front as being for 120/208 1Ø 3W.