Infinity is correct. Also, if you are installing a steel box that is less than 16sqin, you most likely do not need to do anything additional if the ceiling rating is 2hr or less.
I recall steel boxes have a 1.5 hr rating so in a 2 hr assembly additional protection is required to comply with rating--- 2009 IBC code for a general reference
713.3.2 Membrane penetrations. Membrane penetrations shall comply with Section 713.3.1. Where walls or partitions are required to have a
fire-resistance rating, recessed fixtures shall be installed such that the required fire-resistance will not be reduced.
Exceptions:
1. Membrane penetrations of maximum 2-hour fire-resistance-rated walls and partitions by steel electrical boxes that do not exceed 16 square
inches (0.0103 m2) in area, provided the aggregate area of the openings through the membrane does not exceed 100 square inches (0.0645 m2) in any
100 square feet (9.29 m2) ofwall area. The
annular space between the wall membrane and the box shall not exceed l/S inch (3.1 mm). Such boxes on
opposite sides ofthe wall or partition shall be separated by one of the following:
1.1. By a horizontal distance of not less than 24 inches (610 mm) where the wall or partition is constructed with individual noncommunicating stud cavities;
1.2. Bya horizontal distance of not less than the depth ofthe wall cavity where the wall cavity is filled with cellulose loose-fill, rockwool or slag mineral wool insulation;
1.3. By solid fireblocking in accordance with Section 717.2.1;
1.4. By protecting both outlet boxes with
listed putty pads; or 1.5. By other
listed materials and methods.
2. Membrane penetrations by
listed electrical boxes of any material, provided such boxes have been tested for use in fire-resistance-rated assemblies
and are installed in accordance with the instructions included in the listing. The
annular space between the wall membrane and the box shall not
exceed l/S inch (3.1 mm) unless
listed otherwise. Such boxes on opposite sides of the wall or partition shall be separated by one of the following:
2.1. By the horizontal distance specified in the listing of the electrical boxes;
2.2. By solid fireblocking in accordance with Section 717.2.1;
2.3. By protecting both boxes with
listed putty pads; or
2.4. By other
listed materials and methods.
3. Membrane penetrations by electrical boxes of any size or type, which have been
listed as part of a wall opening protective material system for use in fire-resistance-rated assemblies and are installed in accordance with the instructions included in the listing.
4. Membrane penetrations by boxes other than electrical boxes, provided such penetrating items and the
annular space between the wall membrane and the box, are protected by an
approved membrane penetration firestop system installed as tested in accordance with ASTM E 814 or UL 1479, with a minimum positive pressure differential of 0.01 inch (2.49 Pa) of water, and shall have an F and T rating of not less than the required
fire-resistance rating of the wall penetrated and be installed in accordance with their listing.
5. The
annular space created by the