    Is it allowed to use multiple conductors as grounding conductors? According to UL508A Table 75.1 minimum conductors size for 800A service disconnect is 2/0 (copper); can I use 2X2AWG instead?
    "Because it's there!"
    George Mallory
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,016
    I am unaware of any code stating the grounding electrode conductor cannot be paralleled. In a 400 amp service with 2 -200 amp discos we are allowed to run 2-#4's to the electrode(s). I am unaware of what UL 508A is stating.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #3
    Join Date
    Aug 2010
    Texas
    Posts
    284
    Quote Originally Posted by Dennis Alwon View Post
    Thanks. I also read UL508A and did not see anything against paralleling grounding conductors.
    George Mallory
  4. #4
    Join Date
    Jul 2006
    Posts
    7,636
    I would still assume the same rules apply as to CCCs, i.e. not smaller than 1/0.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...
  5. #5
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,016
    Quote Originally Posted by Jraef View Post
    That section does not refer to grounding electrode conductor's
  6. #6
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    There is no section which says you can parallel a GEC using smaller conductors. So you want to parallel 'em. Okay... each has to be the required minimum size.
    I will have achieved my life's goal if I die with a smile on my face.
  7. #7
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,534
    The grounding electrode conductor is not part of the UL 508a panel. It is field wiring.
    Bob
  8. #8
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,959
    Quote Originally Posted by Smart $ View Post
    I agree, there is nothing in table 250.66 that states that you can use something other than the size GEC listed in the table.
    Rob
  9. #9
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,016
    I thought the code was permissive---if it does say you can't then you can....you all are changing the rules....LOL
  10. #10
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,016
    Tell me this. I can run a smaller conductor for 2- 200 amp panels to each disconnect and be compliant. Can I run those separate grounding electrode conductor's (#4's) to the same meter instead of the disconnect? If I can run it to the disconnect why can't I run it to the meter instead? Seems no different than a parallel grounding electrode conductor.
    I have never done it but I can't seem to find where it may be non compliant.
    This may be a reason not to parallel.
    C) Continuous. Except as provided in 250.30(A)(5) and
    (A)(6), 250.30(B)(1), and 250.68(C), grounding electrode
    conductor(s) shall be installed in one continuous length
    without a splice or joint. If necessary, splices or connections
    shall be made as permitted in (1) through (4):
    (1) Splicing of the wire-type grounding electrode conductor
    shall be permitted only by irreversible compression type
    connectors listed as grounding and bonding equipment
    or by the exothermic welding process.
    (2) Sections of busbars shall be permitted to be connected
    together to form a grounding electrode conductor.
    (3) Bolted, riveted, or welded connections of structural
    metal frames of buildings or structures.
    (4) Threaded, welded, brazed, soldered or bolted-flange
    connections of metal water piping.
Posting Permissions