    Have seen this a couple of times now with ground mounted PV systems...standard 5/8" x 8' ground rod inserted into one of the footings for the ground mount post system. I have concerns that this is not an accepted grounding electrode conductor by definition of either a rod electrode (not in direct contact with soil) or a concrete encased electrode (concrete is not in direct contact with earth as it is encased by a sonotube). Am I missing anything here?
  2. #2
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,704
    If the rod is below grade the concrete would enhance performance though it still doesn't meet CEE requirements. But don't sound like that is what you have.