Results 1 to 6 of 6
Thread: NM cable (romex). Sleeved thru Sealtight to roof Condensor.
  1. #1
    Join Date
    Apr 2009
    Posts
    246
    NM I was told cant be used in sealtight. On exterior condensors. It must enter rear of disconnect. And I cant sleeve 8 feet.
    Where is that code. Is it true.
  2. #2
    Join Date
    Mar 2003
    New England
    Posts
    13,287
    You cannot install NM cable in a wet locations. Technically, the inside of any outdoor raceway is considered a wet location including flexible conduit. So technically you have to use THWN or equivalent conductors.
    I don't know the exact code article, but someone else will provide it. I know it's a pain even if you have a short sleeve going to a disconnect, but it's still the code. Not saying I'm perfect in this regard though.
  3. #3
    Join Date
    Mar 2010
    Lake of the Ozarks
    Posts
    1,034
    300.38
    334.12(B)(4)
    1N73LL1G3NC3 15 7H3 4BILI7Y 70 4D4P7 70 CH4NG3.
  4. #4
    Join Date
    Feb 2003
    Illinois
    Posts
    23,577
    Quote Originally Posted by luckylerado View Post
    300.38
    334.12(B)(4)
    300.38 never applies to NM.
    300.9 does.
    Don, Illinois
    Ego is the anesthesia that deadens the pain of stupidity. Dr. Rick Rigsby
    (All code citations are 2017 unless otherwise noted)
  5. #5
    Join Date
    Mar 2010
    Lake of the Ozarks
    Posts
    1,034
    Quote Originally Posted by don_resqcapt19 View Post
    300.9 does.
    Over 1000V. Good catch but literally exactly the same language.
  6. #6
    Join Date
    Feb 2003
    Illinois
    Posts
    23,577
    Not really, I wrote 300.9.
    Don, Illinois
Posting Permissions
  • You may not post replies
  • You may not edit your posts