Thread: panel board as an EGC

  1. #31
    Join Date
    Feb 2013
    Location
    Aspen, Colo
    Posts
    1,907
    Quote Originally Posted by JJspark View Post
    I talked to the inspector today about this. He said it is not UL listed to be an EGC.
    State Inspector?
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.

  2. #32
    Join Date
    Nov 2010
    Location
    Fort Collins, Colorado
    Posts
    2,365
    Quote Originally Posted by JJspark View Post
    I talked to the inspector today about this. He said it is not UL listed to be an EGC.
    As I ponder this further, the more absurd it is. Let's try another example. Let's say you have sub panel fed with a metallic raceway that qualifies as an EGC and you have no wire type EGC in the feeder. Then you add branch circuits that have a wire type EGC so you add a factory ground bar kit to land them on. It should be obvious that whether you have 1 or 4 ground bars with a jumper between them the enclosure will still have to carry the short circuit current back to the feeder conduit. I would ask this inspector would he require a bonding jumper if you only had 1 ground bar and if so where would you connect each end?

  3. #33
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    22,826
    Quote Originally Posted by JJspark View Post
    I talked to the inspector today about this. He said it is not UL listed to be an EGC.
    Well he's incorrect, now is up to you to decide if you want to fight him on it by going over his head or just add the jumpers. What size jumpers did he say that you're "required" to use?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #34
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    31,312
    Quote Originally Posted by JJspark View Post
    I talked to the inspector today about this. He said it is not UL listed to be an EGC.
    He might be correct, only because it was never tested for that specific purpose, but no real need to if NEC recognizes it as being suitable to use as part of the EGC path.

  5. #35
    Join Date
    May 2011
    Posts
    3,490
    Quote Originally Posted by petersonra View Post
    where does it say in the code that metal boxes have to be listed?
    250.118.

    It doesn't have to be listed to use it as a box, but it has to be listed if you want to use it as an EGC. That is, if it's not one of the other items identified in that section.

  6. #36
    Join Date
    Apr 2007
    Location
    Berkeley, CA
    Posts
    1,187
    There's a fundamental conflict between the definition of EGC, 250.118, and common practice:

    (2017) Grounding Conductor, Equipment The conductive path(s) that provides a ground-fault current path and connects normally non-current-carrying metal parts of equipment together and to the system grounded conductor or to the grounding electrode conductor, or both.

    (2017) 250.118 Types of Equipment Grounding Conductors. The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more of a combination of the following:

    Now "metallic equipment enclosures" clearly "enclose circuit conductors" yet are not listed in 250.118. But common practice is to rely on metallic equipment enclosures as a component of the "ground-fault current path". Hence the conflict.

    This could easily be resolved by adding "metallic equipment enclosures" to the list in 250.118. Right now everyone behaves as if that were the case.

    Cheers, Wayne

  7. #37
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    2,895
    Quote Originally Posted by JJspark View Post
    I talked to the inspector today about this. He said it is not UL listed to be an EGC.
    If the enclosure is not UL listed to be EGC then essentially what he requires is all of the metallic conduits to have a grounding bushings as they enter the enclosure.
    Edward
    Education is a progressive discovery of our ignorance.


  8. #38
    Join Date
    Apr 2003
    Location
    Planet macmikeman
    Posts
    3,330
    250.96 (A) specifically mentions enclosures, which allows the practice .


    I think this is merely a case of that inspector once read that the building steel is not to be used as a bonding path. A panel board is not '' building steel'', but of course many inspectors once countered with that will begin with the '' we interpret this to mean the panel boards are what this is referring to.....