Page 4 of 6 FirstFirst ... 23456 LastLast
Results 31 to 40 of 58
Thread: panel board as an EGC
  1. #31
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,979
    Quote Originally Posted by JJspark View Post
    I talked to the inspector today about this. He said it is not UL listed to be an EGC.
    State Inspector?
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.
  2. #32
    Join Date
    Nov 2010
    Fort Collins, Colorado
    Posts
    2,597
    As I ponder this further, the more absurd it is. Let's try another example. Let's say you have sub panel fed with a metallic raceway that qualifies as an EGC and you have no wire type EGC in the feeder. Then you add branch circuits that have a wire type EGC so you add a factory ground bar kit to land them on. It should be obvious that whether you have 1 or 4 ground bars with a jumper between them the enclosure will still have to carry the short circuit current back to the feeder conduit. I would ask this inspector would he require a bonding jumper if you only had 1 ground bar and if so where would you connect each end?
  3. #33
    Join Date
    Jul 2003
    New Jersey
    Posts
    24,724
    Well he's incorrect, now is up to you to decide if you want to fight him on it by going over his head or just add the jumpers. What size jumpers did he say that you're "required" to use?
    Rob
  4. #34
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    35,668
    He might be correct, only because it was never tested for that specific purpose, but no real need to if NEC recognizes it as being suitable to use as part of the EGC path.
  5. #35
    Join Date
    May 2011
    Posts
    4,053
    Quote Originally Posted by petersonra View Post
    where does it say in the code that metal boxes have to be listed?
    250.118.
    It doesn't have to be listed to use it as a box, but it has to be listed if you want to use it as an EGC. That is, if it's not one of the other items identified in that section.
  6. #36
    Join Date
    Apr 2007
    Berkeley, CA
    Posts
    1,587
    There's a fundamental conflict between the definition of EGC, 250.118, and common practice:
    (2017) Grounding Conductor, Equipment The conductive path(s) that provides a ground-fault current path and connects normally non-current-carrying metal parts of equipment together and to the system grounded conductor or to the grounding electrode conductor, or both.
    (2017) 250.118 Types of Equipment Grounding Conductors. The equipment grounding conductor run with or enclosing the circuit conductors shall be one or more of a combination of the following:
    Now "metallic equipment enclosures" clearly "enclose circuit conductors" yet are not listed in 250.118. But common practice is to rely on metallic equipment enclosures as a component of the "ground-fault current path". Hence the conflict.
    This could easily be resolved by adding "metallic equipment enclosures" to the list in 250.118. Right now everyone behaves as if that were the case.
    Cheers, Wayne
  7. #37
    Join Date
    Feb 2003
    Somewhere over the rainbow
    Posts
    3,279
    If the enclosure is not UL listed to be EGC then essentially what he requires is all of the metallic conduits to have a grounding bushings as they enter the enclosure.
    Edward
    The only thing I know, is the progressive discovery of my ignorance
  8. #38
    Join Date
    Apr 2003
    Planet macmikeman
    Posts
    3,434
    250.96 (A) specifically mentions enclosures, which allows the practice .
    I think this is merely a case of that inspector once read that the building steel is not to be used as a bonding path. A panel board is not '' building steel'', but of course many inspectors once countered with that will begin with the '' we interpret this to mean the panel boards are what this is referring to.....
    85deg. an Sunny today.
  9. #39
    Join Date
    Jun 2017
    Jupiter
    Posts
    24
    Quote Originally Posted by wwhitney View Post
    Cheers, Wayne
    I kind of agree with you. BTW - They don't use the term "metallic" anymore - now they will only use the term "metal." I'm going to try to add that like you say.
    This debate has gone on for far too long and it should be made much clearer in the code one way or the other. I should point out that nobody here in this forum saw what the inspector saw. If the EC attempted to use a different ground bar (one that is not listed for that particular panel) or if they didn't use the factory threads, of if they didn't use the correct machine screws, the inspector would be 100% correct in requiring the bonding jumper. So while it is easy to generalize, in all reality - we just don't know.
    Got to run, thanks.
  10. #40
    Join Date
    Oct 2015
    US
    Posts
    453
    How many panels, cabinets have provisions for multiple egc bars? I have seen some with 2 different possible mounting locations, if you install an EGC bar say with self tappers anywhere wouldn't that voilate the ul listing of that can by not using it the way it was intended?
    Sent from my SM-G950U using Tapatalk
Posting Permissions
  • You may not post replies
  • You may not edit your posts