    Hello I'm having trouble determining whether to model EMT as magnetic or non-magnetic in short circuit calculations as I know this will have an impact on an overall cable's impedance.
    Is the majority of EMT out there magnetic rather than non magnetic or vice versa? Does the conduit being rigid or not play a role? Most of the time in the feeder schedules I am given show whether it's PVC or EMT and if it's rigid or not. Any tricks for how to make a sound assumption based on that information? Your help would be appreciated. Thanks!
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    32,868
    Welcome to the forum
    All the emt I have seen is magnetic.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #3
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,175
    Quote Originally Posted by Dennis Alwon View Post
    Isn't there aluminum EMT?
  4. #4
    Join Date
    Dec 2010
    Posts
    1,369
    Quote Originally Posted by ggunn View Post
    Yes
    http://www.americanconduit.com/produ...ubing-emt.html
    The more they overthink the plumbing, the easier it is to stop up the drain
  5. #5
    Join Date
    Mar 2008
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,770
    Yes.
    Cheers and Stay Safe,
    Marky the Sparky
  6. #6
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,175
    Well then, unless you have an aluminum magnet...
  7. #7
    Join Date
    Jul 2006
    Posts
    2,555
    Quote Originally Posted by ish1284 View Post
    Assume that EMT will be regular steel, and thus magnetic. Stainless-steel and aluminum EMT do exist, but they would be called out in a spec.
    No, only the metal composition.
  8. #8
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    32,868
    Yes, there is but that is not a standard install.
  9. #9
    Join Date
    Feb 2003
    New York, 40.7514,-73.9925
    Posts
    4,439
    We typically model raceway as non-magnetic unless we know for sure it is magnetic.
    Non-magnetic will provide worst case short circuit values. Arc Flash incident energies might end up not be worst case (higher fault current makes OCPDs open faster, thus sometimes lower level PPE called out), but you need to pick your poison.