    Magnetic vs. non-magnetic EMT

    Hello I'm having trouble determining whether to model EMT as magnetic or non-magnetic in short circuit calculations as I know this will have an impact on an overall cable's impedance.

    Is the majority of EMT out there magnetic rather than non magnetic or vice versa? Does the conduit being rigid or not play a role? Most of the time in the feeder schedules I am given show whether it's PVC or EMT and if it's rigid or not. Any tricks for how to make a sound assumption based on that information? Your help would be appreciated. Thanks!

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    31,667
    Welcome to the forum

    All the emt I have seen is magnetic.

  3. #3
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    7,533
    Quote Originally Posted by Dennis Alwon View Post
    Welcome to the forum

    All the emt I have seen is magnetic.
    Isn't there aluminum EMT?

  4. #4
    Join Date
    Dec 2010
    Posts
    1,116
    Quote Originally Posted by ggunn View Post
    Isn't there aluminum EMT?
    Yes

    http://www.americanconduit.com/produ...ubing-emt.html
    The more they overthink the plumbing, the easier it is to stop up the drain

  5. #5
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    8,943
    Quote Originally Posted by ggunn View Post
    Isn't there aluminum EMT?
    Yes.

    http://www.americanconduit.com/produ...ubing-emt.html
    Cheers and Stay Safe,

    Marky the Sparky

  6. #6
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    7,533
    Well then, unless you have an aluminum magnet...

  7. #7
    Join Date
    Jul 2006
    Posts
    2,246
    Quote Originally Posted by ish1284 View Post
    Is the majority of EMT out there magnetic rather than non magnetic or vice versa?
    Assume that EMT will be regular steel, and thus magnetic. Stainless-steel and aluminum EMT do exist, but they would be called out in a spec.

    Quote Originally Posted by ish1284 View Post
    Does the conduit being rigid or not play a role?
    No, only the metal composition.

  8. #8
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    31,667
    Quote Originally Posted by ggunn View Post
    Isn't there aluminum EMT?

    Yes, there is but that is not a standard install.

  9. #9
    Join Date
    Feb 2003
    Location
    New York, 40.7514,-73.9925
    Posts
    4,163
    We typically model raceway as non-magnetic unless we know for sure it is magnetic.

    Non-magnetic will provide worst case short circuit values. Arc Flash incident energies might end up not be worst case (higher fault current makes OCPDs open faster, thus sometimes lower level PPE called out), but you need to pick your poison.
    Ron