Results 1 to 6 of 6
Thread: Ground Enhancement Material use in a grounding network
  1. #1
    Join Date
    Jul 2016
    Austin, Texas, USA
    Posts
    10
    Had an engineer tell me that ground enhancement material must be used on the bare grounding conductors that are interconnecting ground plates and not just the ground plates in order to achieve the desired resistance to ground in a grounding network. Thoughts? Opinions? Facts?
  2. #2
    Join Date
    Aug 2004
    Northern illinois
    Posts
    15,827
    Quote Originally Posted by t_van View Post
    might be true. depends on the earth properties and what the desired resistance is.
    Bob
  3. #3
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    18,797
    But, on the other hand, the total area of the bonding conductors may not be significant unless the runs are long.
    If the area is significant, and the soil itself is poor, then at that point adding enhancement materials would be justified.
  4. #4
    Join Date
    Aug 2004
    Northern illinois
    Posts
    15,827
    if you do what he wants and it does not work it is on him.
    if you do something else and it does not reach the desired resistance, you get to dig up the grounding system and redo it.
    Bob
  5. #5
    Join Date
    Jul 2013
    Resting under the Major Oak UK
    Posts
    1,092
    I assume he was referring to this stuff http://www.cablejoints.co.uk/sub-pro...hing-compounds
    I’ve used it for substation earth nests.
    The reports of my death are greatly exaggerated.
  6. #6
    Join Date
    Dec 2012
    Posts
    18,797
    Quote Originally Posted by Tony S View Post
    Kind of like a CEE without the concrete.
Tags for this Thread
Posting Permissions
  • You may not post replies
  • You may not edit your posts