Hi,

I tapped onto feeder conductors being supplied by a 200A OCPD. I used #3 wire and took them to a 100amp fused disconnect. Is this within code or do I need #3/0 even if I go to the 100A fused disconnect? Will there ever be the possibility of more than 100 amps on those conductors? maybe only in a fault condition, right?

Thanks for your help!
 

Smart $

Esteemed Member
Location
Ohio
You should be good on conductor size (more to compliance than just conductor size).

Don't forget if using a wire-type EGC, it must be sized per 250.122 for the 200A OCPD rating, but not required to be larger than the tap conductors.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I don't see where you mentioned the length of the tap.
The tap would need comply with the rules of 240.21, commonly 25 ft.
 