    service equipment protection

    I have a 1200 amp rated service equipment - six switches as the service disconnecting means -- calculated load is under 1200 amps -- the disconnecting means sum is 1600 amps
    I understand 230.80 conductor sizing in relationship to calculated load but still looking for code allowing equipment that has the bus bar rated below the disconnecting means sum This would follow an example of having a calculated load for an 100 amp rated panel @ 80 amps while using 125 Amp OCPD for the disconnecting means -- 408.36?
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.

  2. #2
    Join Date
    Feb 2013
    Location
    Aspen, Colo
    Posts
    1,909
    77 views & no comments -- certainly this makes some uncomfortable to verify as compliant or violation --
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.

  3. #3
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,267
    combination of 230.42 (conductor size must carry load) and 230.71 (up to 6 disconnects permitted) and 230.79 (service disconnect must be rated as high as load)
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  4. #4
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    31,657
    If panel is only listed as service equipment with a main breaker installed, then that breaker will protect the bus.

    If panel is listed as service equipment as main lug fed with multiple mains, then your bus ampacity is not really being treated any differently then your service conductor ampacity

    Not sure what or if there is code section to cite, just my opinion.

    Have done similar before and was never questioned about it, one I do recall was 800 amp bus, two 400 amp and two 125 amp breakers. Total load calculation probably under 400 amps - but one 400 amp breaker was a spare for future use and anticipated load when that happens was to likely be less then 300.

  5. #5
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    2,768
    230.90(A), Ex. No. 3. is what you are looking for.

  6. #6
    Join Date
    Feb 2013
    Location
    Aspen, Colo
    Posts
    1,909
    Thanks for commenting to conversation
    Panelboard. A single panel or group of panel units designed for assembly in the form of a single panel, including buses and automatic overcurrent devices, and equipped with or without switches for the control of light, heat, or power circuits; designed to be placed in a cabinet or cutout box placed in or against a wall, partition, or other support; and accessible only from the front.
    -- 408.30 clearly states "panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard"
    408.36 Overcurrent Protection
    In addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard. This overcurrent protective device shall be located within or at any point on the supply side of the panelboard.

    Exception No. 1 & 230.80 both
    refer to 230.71 Maximum Number of Disconnects
    Exception No. 1: Individual protection shall not be required for a panelboard used as service equipment with multiple disconnecting means in accordance with 230.71. In panelboards protected by three or more main circuit breakers or sets of fuses, the circuit breakers or sets of fuses shall not supply a second bus structure within the same panelboard assembly.
    230.80 Combined Rating of Disconnects
    Where the service disconnecting means consists of more than one switch or circuit breaker, as permitted by 230.71, the combined ratings of all the switches or circuit breakers used shall not be less than the rating required by 230.79.

    230.79 which only calls out minimum for OCPD as a disconnecting means
    230.79 Rating of Service Disconnecting Means
    The service disconnecting means shall have a rating not less than the calculated load to be carried, determined in accordance with Part III, IV, or V of Article 220, as applicable. In no case shall the rating be lower than specified in 230.79(A), (B), (C), or (D).

    I do not interprete (as of this moment) that the initial statement of 408.30 clearly states "panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard" has been nullified with an exception.
    Attached Images Attached Images  
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.

  7. #7
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    31,832
    If there is one main breaker than the overcurrent protective device must be rated no larger than the panelborad. There are 6 overcurrent protective device's in your scenario. You do not add up the breaker sizes.


    As David posted

    Exception No. 3: Two to six circuit breakers or sets of
    fuses shall be permitted as the overcurrent device to provide
    the overload protection. The sum of the ratings of the
    circuit breakers or fuses shall be permitted to exceed the
    ampacity of the service conductors, provided the calculated
    load does not exceed the ampacity of the service
    conductors.

  8. #8
    Join Date
    Feb 2013
    Location
    Aspen, Colo
    Posts
    1,909
    [QUOTE=Dennis Alwon;1832134]If there is one main breaker than the overcurrent protective device must be rated no larger than the panelborad. There are 6 overcurrent protective device's in your scenario. You do not add up the breaker sizes.



    where does the equipment buss get referenced -- service conductors is stated

    Exception No. 3: Two to six circuit breakers or sets of
    fuses shall be permitted as the overcurrent device to provide
    the overload protection. The sum of the ratings of the
    circuit breakers or fuses shall be permitted to exceed theampacity of the service conductors, provided the calculated
    load does not exceed the ampacity of the service
    conductors.
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.

  9. #9
    Join Date
    Feb 2003
    Location
    Connecticut
    Posts
    2,768
    Quote Originally Posted by mwm1752 View Post
    where does the equipment buss get referenced -- service conductors is stated
    If there is no main, then the equipment buss is, by definition, service conductors.

  10. #10
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    20,484
    Quote Originally Posted by mwm1752 View Post
    ...
    I do not interprete (as of this moment) that the initial statement of 408.30 clearly states "panelboard shall be protected by an overcurrent protective device having a rating not greater than that of the panelboard" has been nullified with an exception.
    The individual protection noted in 408.36 Exception No. 1 is the protection noted in the general statement. I realize you are saying the multiple protection afforded by the up-to-six disconnecting means exceeds the panelboard [bus] rating. However, if the protection device is not required the condition it not be greater than the panelboard rating is rendered moot by logical deduction.

    Requirements for equipment on the supply side of service disconnecting means relies solely on they be rated not less than the calculated load. No overcurrent device will protect service conductors during a fault condition on the supply side.
    I'll never get there. No matter where I go, I'm always here.