    Condit fill calculations

    I'm confused on the tables and annex c part of the nec.

    Say I have the following....

    All THHN in a schedule 80 pvc
    #12 x10
    #10 x5
    #8 x3

    Since I have over 2 wires in one conduit do I calculate the cross sectional area of the conduit at 40% and then add up cross sectional area of each wire and add them up and see what size the Will fit into?

  2. #2
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,075
    First start on Table 5 ch9
    find THHN row and use Approximate area square inches.
    then add the total of all of the conductors of your example.

    Then go to raceway properties Table 4 of ch9
    Find rigid PVC conduit
    scroll down the 40% column until you find a number that is higher than the total area that you calculated.
    then look to the left of that row you will see what conduit is needed.

    Added: Based on my calculation you need a 1.25" conduit
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  3. #3
    Join Date
    Jan 2013
    Location
    Wa state
    Posts
    375
    That's pretty much what I was thinking. Thank you for the clarification. Does the annex c take the 40% into consideration when it states the maximum number of conductors in any given raceway?

  4. #4
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,006
    Quote Originally Posted by crtemp View Post
    That's pretty much what I was thinking. Thank you for the clarification. Does the annex c take the 40% into consideration when it states the maximum number of conductors in any given raceway?
    A

    Annex C is only used when all the conductors are the same size with the same insulation. It is based on the table for 1 wire (53%), 2 wires(31%) or over 2 wires (60%)

  5. #5
    Join Date
    May 2013
    Location
    Massachusetts
    Posts
    2,193
    Quote Originally Posted by Dennis Alwon View Post
    A

    Annex C is only used when all the conductors are the same size with the same insulation. It is based on the table for 1 wire (53%), 2 wires(31%) or over 2 wires (40%)
    Corrected.

    Essentially, it represents about 70% of the conduit diameter filled with cable, if you were to pack the cables as tightly as possible. Since two circles have a lousy packing factor in a circle, the area fill percentage is significantly less for 2 wires. 1 circle obviously has a 100% packing factor in a circle, so its area fill percentage is high. Then when you look at 3+ circles in a circle, the packing factor takes off to a steady cruising value between 80% & 90%.

  6. #6
    Join Date
    Jan 2013
    Location
    Wa state
    Posts
    375
    Anyone see issues with running two thhn #4`s and one thhn #8 in 3/4'' EMT?

  7. #7
    Join Date
    Jul 2003
    Location
    MA
    Posts
    2,000
    Quote Originally Posted by crtemp View Post
    Anyone see issues with running two thhn #4`s and one thhn #8 in 3/4'' EMT?
    What does the fill % calculate to?
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices

  8. #8
    Join Date
    Jan 2013
    Location
    Wa state
    Posts
    375
    Quote Originally Posted by tkb View Post
    What does the fill % calculate to?
    Wire totals to .2014 in sq and 3/4'' EMT is .213 in sq at 40%

    Just want to make sure I'm not missing something.

  9. #9
    Join Date
    Jul 2003
    Location
    MA
    Posts
    2,000
    Quote Originally Posted by crtemp View Post
    Wire totals to .2014 in sq and 3/4'' EMT is .213 in sq at 40%

    Just want to make sure I'm not missing something.
    You are correct. It is less than 40%, but not by much, 37.79%
    Personally it would depend on the length and number of bends, but I would go with 1".
    Tim
    Master Electrician
    New England
    Yesterday's Technology at Tomorrow's Prices

  10. #10
    Join Date
    Jan 2013
    Location
    Wa state
    Posts
    375
    Quote Originally Posted by tkb View Post
    You are correct. It is less than 40%, but not by much, 37.79%
    Personally it would depend on the length and number of bends, but I would go with 1".
    Ya for sure. It was super tight when I physically looked at the pipe and wire. After all the parts to do it in EMT I said forget it and just ran 1-1/4" pvc. Much easier.