Liquidtight Flexible Metal Conduit Operating Temperature

Status
Not open for further replies.

xguard

Senior Member
Location
Baton Rouge, LA
350.12 Uses Not Permitted
LFMC shall not be used as follows: (2) Where any combination of ambient and conductor temperature produces an operating temperature in excess of that for which the material is approved.

Can a 75 degree C or 90 degree C conductor be used at it's full ampacity rating if it's installed in LFMC that has a temperature rating of 60 degree C?

If not how would you arrive at the allowable ampacity and ambient temperature it could be used at?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Your circuit ampacity cannot exceed the 60? C rating of the conductors. This would also be after you made any ampacity corrections for ambient temperature if required. So if you use say #8 THHN with 75? C terminations (which has an ampacity of 50 amps) you would still need to limit the circuit to the 60? C ampacity (40 amps) because the 60? C LFMC would be the "weakest link" in the installation.
 