Thread: 2014 210.52(B) - Refrigerator on its' own circuit

  1. #1
    Join Date
    Dec 2003
    Location
    San Francisco Bay Area
    Posts
    552

    2014 210.52(B) - Refrigerator on its' own circuit

    A friend of mine just failed an inspection in a jurisdiction we don't work in. He said that they failed him (he's a GC) because the 2014 210.52(B) requires that the refrigerator be on it's own circuit. I said that I believe the inspector misread the exception that ALLOWS the refrigerator to be on its own circuit. I sent him a cut and past from my 2017 PDF (210.52(B). The inspector told him that the 2017 doesn't matter (I agree) but that the 2014 specifically states the refrigerator must me on its own circuit. I don't have my 2014 copy here. Did I miss something in 2014? Anybody care to cut and past a copy of the 2014?

    Thanks

  2. #2
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    31,667
    Inspector is incorrect. If you use a separate circuit for a refrigerator then it can be on a 15 amp circuit otherwise, it is part of the small appliance branch circuit. Now Calif. may have some amendments.

  3. #3
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    18,457
    The 2013 edition of the California Electrical Code (i.e., the current edition) does not alter the language in the NEC for article 210.52(B)(1) and its exception 2. Here is the text:
    Exception No.2: The receptacle outlet for refrigeration equipment shall be permitted to be supplied from an individual branch circuit rated 15 amperes or greater.
    The "shall be permitted" words do not require that the fridge be on a separate circuit. The inspector is wrong, as Dennis has already said.
    Charles E. Beck, P.E., Seattle
    Comments based on 2014 NEC unless otherwise noted.

  4. #4
    Join Date
    Dec 2003
    Location
    San Francisco Bay Area
    Posts
    552
    Thanks Dennis and Charlie. It seemed unlikely that they would have required it in 2014 then went back in 2017, but stranger things have happened.

    Cheers.

  5. #5
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    18,457
    Quote Originally Posted by sfav8r View Post
    It seemed unlikely that they would have required it in 2014 then went back in 2017. . . .
    You mentioned that this project is in a jurisdiction other than that of your own home. Is it still in California? If so, then do keep in mind that the 2014 and 2017 editions of the NEC are not relevant, and I would not mention them to the inspector. The 2013 CEC is all that matters.

    Charles E. Beck, P.E., Seattle
    Comments based on 2014 NEC unless otherwise noted.

  6. #6
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    2,887
    Quote Originally Posted by charlie b View Post
    You mentioned that this project is in a jurisdiction other than that of your own home. Is it still in California? If so, then do keep in mind that the 2014 and 2017 editions of the NEC are not relevant, and I would not mention them to the inspector. The 2013 CEC is all that matters.

    The CEC 2013 is relatively the same as the 2014 NEC.

    So far my experience with CA inspectors has been then usually refer back to the NEC instead of the CEC.
    Edward
    Education is a progressive discovery of our ignorance.


  7. #7
    Join Date
    Feb 2003
    Location
    San Jose, CA
    Posts
    1,368
    Quote Originally Posted by edward View Post
    The CEC 2013 is relatively the same as the 2014 NEC.

    So far my experience with CA inspectors has been then usually refer back to the NEC instead of the CEC.
    I agree. There is very little difference between the NEC and CEC. I have never had an inspector reference the CEC.

    While the NEC and CEC don't directly specify a dedicated circuit for refrigerators the instruction for all of the built-in type (sub-Zero, Viking, etc.) specify a dedicated circuit.
    Curt Swartz
    Electrical Contractor

  8. #8
    Join Date
    Apr 2007
    Location
    Berkeley, CA
    Posts
    1,187
    Quote Originally Posted by charlie b View Post
    ]The 2013 edition of the California Electrical Code (i.e., the current edition)
    I believe the current version is the 2016 California Electrical Code, based on the 2014 NEC.

    Cheers, Wayne