Thread: Pool Pump Gfci

  1. #11
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,241
    Quote Originally Posted by GoldDigger View Post
    If you do not believe that all three circuits developed leaky loads at the same time, I guess it is more probable that something happened to the feeder neutral that also created a spurious ground to neutral bond upstream of the breakers.
    Or all three have been leaking for a long time but there was no solid EGC connection to carry the leakage current.

    Sent from my XT1585 using Tapatalk
    I hope that is not true as my guys installed the feeder. That is what I am going to check out.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  2. #12
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,744
    I do not believe GFCIs need a solid EGC connection to work. All they need is a path. Ants, water, dew, flesh, etc.
    Tom
    TBLO

  3. #13
    Join Date
    May 2017
    Location
    US
    Posts
    1
    Pool pumps do not require GFI.... Right?

    Sent from my XT1058 using Tapatalk

  4. #14
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,241
    Quote Originally Posted by ptonsparky View Post
    I do not believe GFCIs need a solid EGC connection to work. All they need is a path. Ants, water, dew, flesh, etc.
    Gfci do not need an equipment grounding conductor to work
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  5. #15
    Join Date
    Dec 2006
    Location
    Chapel Hill, NC
    Posts
    32,241
    Quote Originally Posted by robertsledzaus80 View Post
    Pool pumps do not require GFI.... Right?

    Sent from my XT1058 using Tapatalk
    No
    t correct. It has been many code cycles where swimming pool motors have been required to have gfci depending if they were 20 amps or less. Now all single phase pool motors need gfci protection

    680.21(C) GFCI Protection. Outlets supplying pool pump motors
    connected to single-phase, 120-volt through 240-volt branch
    circuits, whether by receptacle or by direct connection, shall be
    provided with ground-fault circuit-interrupter protection for
    personnel.

    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky



  6. #16
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    18,150
    Quote Originally Posted by Dennis Alwon View Post
    Gfci do not need an equipment grounding conductor to work
    But to the extent that there is no alternate grounding path there may not be enough current to trip a GFCI.
    Admittedly that is far less likely when you also have an equipotential grid present, as with a pool.

    Sent from my XT1585 using Tapatalk