    Quote Originally Posted by dj94 View Post
    thanks Guys,
    the EE is still insisting on doing it the wrong way (his way) he did re issue the response to at lease use the same phase from each panel so hopefully the lights wont explode when the test button is pushed.
    (i kind of hope they do)
    Is there an inspector that could get involved?

    Roger
    Moderator

  2. #12
    Join Date
    Dec 2010
    Posts
    1,150
    It doesn't make any sense. If he can pull a phase, he can pull a neutral as well. I wouldn't sit back and let him do it that way.
    The more they overthink the plumbing, the easier it is to stop up the drain

  3. #13
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,243
    Quote Originally Posted by dj94 View Post
    thanks Guys,
    the EE is still insisting on doing it the wrong way (his way) he did re issue the response to at lease use the same phase from each panel so hopefully the lights wont explode when the test button is pushed.
    (i kind of hope they do)
    No way I would do this. He's an EE not a diety. Tell him no, or tell his boss or somebody what is going on.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  4. #14
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    20,614
    Quote Originally Posted by dkidd View Post
    Where did MWBC sneak in?
    OP say the EE wants two hots to share a single neutral. To do so, it must be a multiwire branch circuit.... right?
    I'll never get there. No matter where I go, I'm always here.

  5. #15
    Join Date
    Jul 2015
    Location
    Colville, WA
    Posts
    347
    But 2 hots from different panels sharing a neutral? Hmmm!

  6. #16
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    20,614
    Quote Originally Posted by Johnnybob View Post
    But 2 hots from different panels sharing a neutral? Hmmm!
    Not permitted. That's why I posted 210.4 in its entirety above.
    I'll never get there. No matter where I go, I'm always here.

  7. #17
    Join Date
    Dec 2010
    Posts
    1,150
    Quote Originally Posted by dj94 View Post
    thanks Guys,
    the EE is still insisting on doing it the wrong way (his way) he did re issue the response to at lease use the same phase from each panel so hopefully the lights wont explode when the test button is pushed.
    (i kind of hope they do)
    If he used the same phase, the neutral current could double.
    The more they overthink the plumbing, the easier it is to stop up the drain

  8. #18
    Join Date
    Dec 2010
    Posts
    1,150
    Quote Originally Posted by Smart $ View Post
    OP say the EE wants two hots to share a single neutral. To do so, it must be a multiwire branch circuit.... right?
    I want to see the handle tie he uses.
    The more they overthink the plumbing, the easier it is to stop up the drain