Results 1 to 9 of 9
Thread: Electric Boiler Disconnect
  1. #1
    Join Date
    Feb 2010
    Posts
    837
    Im adding a 240 kW electric boiler to an independent of the existing electric service. This will be fed from the transformer, to an exterior 700A fused disconnect, and then to an electric boiler located inside the building.
    Having an interior non-fused disconnect for service may be an issue due to space because it will be rated for 800A. Anyone see any issue with requiring the exterior disconnect to be lockable in the open position and then providing signage at the boiler notating its power source to eliminate the requirement for an additional disconnect at the boiler itself?
    I was thinking of adding a shunt trip inside but this may get expensive.
    PS> No, a gas boiler is not an option :-)
  2. #2
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,813
    Disconnect not within sight should be acceptable if lockable.
    Is your second service disconnecting means grouped with the other service disconnecting means?
  3. #3
    Join Date
    Feb 2010
    Posts
    837
    Quote Originally Posted by kwired View Post
    Perfect, just wanted confirmation. Yes, both disconnects are side by side with independent runs to the transformer.
  4. #4
    Join Date
    Jan 2016
    PA
    Posts
    4,889
    Shunt trip expensive?
    what part of the country is this going?
    elec bill may 20K/yr
    use propane until ng available?
    800,000 btu boiler
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,813
    Shunt trip may still be a consideration if you need to have a EPO near the boiler.
  6. #6
    Join Date
    Feb 2010
    Posts
    837
    Quote Originally Posted by Ingenieur View Post
    800,000 btu boiler
    Natural gas is available but appearently a gas fired boiler requires the building to be modified to house a gas fired boiler. Appearently this boiler is only used 3 hours a week to create steam used for brewing processes.
  7. #7
    Join Date
    Feb 2010
    Posts
    837
    I was planning on using a fused disconnect. I know there is a shunt trip fused disconnect but not sure how common they are?
  8. #8
    Join Date
    Jul 2005
    Tennessee
    Posts
    15,550
    You also might want to look a Art 424, likely Part VII, to make sure you have all those bases covered.
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.
  9. #9
    Join Date
    Feb 2010
    Posts
    837
    Quote Originally Posted by augie47 View Post
    Will do, thanks.
    I wonder if I have to take this at 125%? That would put me at a 1000A rated disconnect. It's not continuous but I think it may qualify as a storage heater but not sure of the storage capacity.