Thread: mobile home

  1. #1
    Join Date
    Feb 2016
    Location
    winchester, NH
    Posts
    1

    mobile home

    I ran conduit from a 100 amp disconnect on a pedestal to the corner of the mobile home, 90 elbow up to an LB, sawed a hole in the skirting and glued a 12 inch nipple through to underneath the mobile home. I ran #2, 4 wire URD through conduit from the disco to the LB ounce under the mobile home, I ran the 4 wire up high, I supported the URD to the bottom of the home up off the pad. was told by a local inspector that the feeder wires needed to be in a conduit under the mobile home all the way to the Panel, where in the 2017 code book can i find this? Thanks Jeff

  2. #2
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    21,385
    URD is not an NEC recognized cable type. It must be dual listed as an NEC-recognized type. Permitted and not permitted uses will depend on type. It is quite common for URD to be dual listed as USE-2. You can't run USE above ground except to terminate where it emerges and even that has to be outside [338.12(B)(2)]. Now if the individual conductors happen to be marked XHH*, you can run it above ground in conduit.
    I will have achieved my life's goal if I die with a smile on my face.

  3. #3
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,773
    Putting aside the URD naming issue since most of it is dual rated, 300.3 means that you can't run exposed conductors, they have to be in a cable assembly or in conduit.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  4. #4
    Join Date
    Jan 2008
    Location
    Raeford, NC
    Posts
    3,679
    Look at 550.10 (G) also
    Organized people are people that are just too lazy to look for their stuff

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,530
    Quote Originally Posted by ActionDave View Post
    Putting aside the URD naming issue since most of it is dual rated, 300.3 means that you can't run exposed conductors, they have to be in a cable assembly or in conduit.
    Or with the USE rating - direct buried at a depth that complies with 300.5.

  6. #6
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,773
    Quote Originally Posted by kwired View Post
    Or with the USE rating - direct buried at a depth that complies with 300.5.
    Since the OP is talking about a mobile home I am of the mind to say he is using URD as a slang term, like so many of us do, and what he really has is mobile home feeder that is direct bury rated and is allowed to be used inside.
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  7. #7
    Join Date
    Jun 2006
    Location
    Ohio
    Posts
    21,385
    Quote Originally Posted by ActionDave View Post
    Since the OP is talking about a mobile home I am of the mind to say he is using URD as a slang term, like so many of us do, and what he really has is mobile home feeder that is direct bury rated and is allowed to be used inside.
    Perhaps he'll enlighten us...
    I will have achieved my life's goal if I die with a smile on my face.

  8. #8
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,530
    Quote Originally Posted by ActionDave View Post
    Since the OP is talking about a mobile home I am of the mind to say he is using URD as a slang term, like so many of us do, and what he really has is mobile home feeder that is direct bury rated and is allowed to be used inside.
    I agree, but it still is for direct burial or use in a raceway and not as an exposed wiring method.

    Seen it used exposed several times myself, worse yet enclosed in building finish with no raceway like it were a NM or SE cable.

  9. #9
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,773
    Quote Originally Posted by kwired View Post
    I agree, but it still is for direct burial or use in a raceway and not as an exposed wiring method.

    Seen it used exposed several times myself, worse yet enclosed in building finish with no raceway like it were a NM or SE cable.
    So what's your point, that the OP should bury the mobile home to a depth of twenty four inches?
    Once in a while you get shown the light
    In the strangest of places if you look at it right. Robert Hunter

  10. #10
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,530
    Quote Originally Posted by ActionDave View Post
    So what's your point, that the OP should bury the mobile home to a depth of twenty four inches?
    would solve one problem but create others