    I would like it to be mandatory for manufacturers to put information specs in how electrical is to be connected if they choose not to provide box lug connectors.
    There is a restriction by the component manufacturer as to wire size that is allowed for a binding head terminal. HVAC Equipment manufacturer instructions have one reference the NEC for electrical connections. The photo I attached showing #8 THHN wire is not approved by the component manufacturer.
    http://imageshack.com/a/img924/8837/sLLcUF.jpg
  2. #2
    Join Date
    Jun 2017
    San Clemente
    Posts
    12
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
  3. #3
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,045
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    generally UL requires this information be included in the instructions.
    Bob
  4. #4
    Join Date
    Jun 2017
    San Clemente
    Posts
    12
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This illustrates how we hook up larger than #10 wire to these terminals.
    http://imageshack.com/a/img923/3762/DcLvJR.jpg
  5. #5
    Join Date
    Jun 2017
    San Clemente
    Posts
    12
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by petersonra View Post
    Its not, and I agree it should be required when larger conductors may be in use.
  6. #6
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    34,135
    Mentioned
    3 Post(s)
    Tagged
    0 Thread(s)
    The question is why is a #8 being used on those terminals. Is that the required size or is someone oversizing the circuit? The manufacturer needs to have a terminal sized for the wires needed for their unit. If it is not then letters and phone calls need to be made to the mfgr.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  7. #7
    Join Date
    Jun 2017
    San Clemente
    Posts
    12
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    This same component is used by manufacturer [Lennox Ind. & their subsidiaries] on residential HVAC Equipment 1 - 5 ton. Other manufacturers provide box lug on field hook up side of contactors. I have been harping on this subject with said manufacturer for years with no results. Looks like I have finally found a place to post my story. There are 100's of thousands of units not correctly connected.
    John
  8. #8
    Join Date
    Aug 2004
    Northern illinois
    Posts
    17,045
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    Quote Originally Posted by Jgkopp View Post
    the thing is that the terminal is labeled in some way with the largest size wire that is allowed. I don't know what more you expect of the manufacturer.
    why do you want to use a larger wire than the terminal is rated for?
    what if the terminal is only rated for #10 and someone decides to use 1/0? if that were to happen it is the installers responsibility to figure out how to do it. it is not real hard to splice a #10 conductor to the end of the 1/0 conductor so the #10 can than be connected to the terminal.
    Bob
  9. #9
    Join Date
    Jun 2017
    San Clemente
    Posts
    12
    Mentioned
    0 Post(s)
    Tagged
    0 Thread(s)
    The componet is not labeled with this information. I had to do a lot of digging to get this information.
  10. #10
    Join Date
    Dec 2012
    Placerville, CA, USA
    Posts
    19,943
    Mentioned
    2 Post(s)
    Tagged
    0 Thread(s)
    But at least it is in the product catalog, even if few will read it there.