    Data and Power Cables In Same Access Hole

    I need to know if I can run data and power cable (in flexduit) in same access hole coming through a raised floor?

  2. #2
    Join Date
    Jun 2003
    Location
    Hawthorne, New York NEC: 2014
    Posts
    3,165
    Not sure exactly what you are asking so I'll attempt to answer both interpretations.

    You can't run data in the same duct or raceway with power unless the power is a listed cable.

    If the power is by itself in it's own duct or raceway then there should be no problem with that raceway sharing a hole with LV data.

    -Hal