    Non-Incendive Cl I Div 2

    I am looking at an installation that has AB 1794 IO modules installed in Class I Div 2 area, in a Nema 3R box. The AB 1794 equipment is listed for Class I, Div 2 locations, and the UL CoC lists it as Nonincendive Electrical Equipment.

    My understanding is that Nonincendive electrical equipment can be installed in Class I Div 2 area without a control drawing, and is not required to be supplied from a NI power supply, and circuits connected to the equipment are not necessarily required to be NI.

    For instance - an field device which is explosion-proof is wired to my AB 1794 IO module. The IO Module is NI Equipment. The between the device and the IO module can be installed per 501.10(B) methods, up and until the field device, where I will need a seal fitting and (if needed) explosion-proof fittings between the seal and the device.

    However, if I install a NI field device and wire it to my IO module, then I need to wire per the field device's control drawing, and in accordance with 501.10(B)(3).

    Is this correct?

  2. #2
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,508
    as a practical matter the control drawing exists. it is in the manual for the product. so you can't get rid of it.

    I think you have the right idea about not being required to use a circuit that could be NI as NI.

    I would be careful though in making sure you do not mix NI circuits with normal circuits. I think for instance you might need to use a separate power supply for I/O that are in NI circuits versus ones that are not.
    Bob

  3. #3
    Join Date
    Aug 2011
    Location
    NH
    Posts
    209
    Quote Originally Posted by petersonra View Post
    I would be careful though in making sure you do not mix NI circuits with normal circuits. I think for instance you might need to use a separate power supply for I/O that are in NI circuits versus ones that are not.
    If I install a transmitter that is listed for Cl I Div 2 (non-incendive) - does that listing require installation per the control drawing if I using 501.10(B)(1), (2) (4) wiring methods (i.e. not using provisions of 501.10(B)(3)).