    Quote Originally Posted by Dennis Alwon View Post
    You still need to do the perimeter bonding
    How do you enforce a requirement like this with a portable pool?
    Bob
  2. #12
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,320
    Quote Originally Posted by petersonra View Post
    If the pool meets the definition of storable or portable, then there is no equipotential bonding requirement or perimeter bonding requirement.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #13
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,673
    Quote Originally Posted by JFletcher View Post
    Storable pools do not require an equipotential grid, permanent ones do.
    Where are guys getting that it's a portable pool? OP certainly didn't say that, he only said it was fiberglass. Those fiberglass pools come in a full size and are in-ground pools.
    The only difference (bonding wise) between a fiberglass and metal pool is you don't have to bond the shell itself like you have to do on a metal one, hitting 4 equally spaced points around the pool shell. Also like you would have to do to an above ground pool that is 42" or greater in depth.
    If you aim at nothing, you will hit it every time!
  4. #14
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,801
    Are these kind of pools ul-listed? You would think if so that some kind of bonding means would be required to be part of the pool
    Bob
  5. #15
    Join Date
    Dec 2010
    Tennessee NEC:2008
    Posts
    4,673
    I couldn't tell you if they are listed or not but there is nothing in the shell (fiberglass) that is conductive, so no bonding needed. Now if they add a metal ladder, handrail, etc. then those would need bonding. Also, since the water needs bonding, anything like a metal rail or ladder would accomplish that providing they were bonded to the grid/ring.
  6. #16
    Join Date
    Mar 2014
    Park Ridge, NJ
    Posts
    80
    Quote Originally Posted by Little Bill View Post
    This is true. Not sure about UL listing on these bath tubs-don't do them.
    I am not aware that a pool light fixture or the wet niche if stainless, qualifies for water bonding. A pool heater with a copper/nickel with exchanger does not qualify.
    There a couple of ways to bond the water. One is through the skimmer body. A small drilled allows for a stainless plate with a lug to be fastened. Not a fan especially on concrete pools. After attachment, the skimmer body is encased is concrete making it difficult for future access. Vinyl or fiberglass pools are more accessible.
    My preference is the in-line brass fixture. It has a 1" NPT. I set it after the discharge side of the filter pump. It has a lug connection and is easily accessible. It's looped with the bond wire to the other respective motors and/or equipment.
    These water bond devices WILL corrode at some point. After all, they are in a corrosive condition continually. Throw in the saltwater generators for added corrosion.