    standby generator ground fault protection

    I have an optional standby generator servicing a structure. It is 1500 amps, 480/277. NEC 700.27, 701.27 (emergency systems and required standby) allow ground fault indication but Article 702 has no exception to the ground fault protection requirement for an optional standby generator so ground fault protection must be installed, correct?

  2. #2
    Join Date
    Dec 2015
    Location
    N/A
    Posts
    135
    of course..


    Sent from my iPad using Tapatalk

  3. #3
    Join Date
    Jun 2017
    Location
    WI, USA
    Posts
    323
    Ground fault must be installed as required for feeder/service, no matter. 700/701 allows alarm only. 702 requires trip on ground fault.

  4. #4
    Join Date
    Sep 2017
    Location
    Chicago
    Posts
    4
    The issue of ground fault protection is addressed in NEC Article 700 for emergency generators and in Article 701 for legally required standby generators but there is nothing about ground fault protection in Article 702 for optional standby generators. My question is related to optional standby generator systems.

    Message 3 of 11 (7,440 Views)

  5. #5
    Join Date
    Nov 2015
    Location
    CA, USA
    Posts
    497
    Quote Originally Posted by wyboy View Post
    I have an optional standby generator servicing a structure. It is 1500 amps, 480/277. NEC 700.27, 701.27 (emergency systems and required standby) allow ground fault indication but Article 702 has no exception to the ground fault protection requirement for an optional standby generator so ground fault protection must be installed, correct?
    You are correct. Since 700 and 701 can deal with systems that are life safety they are allowed to continue to operate with a ground fault condition. Art 702 systems have to trip on ground fault.

  6. #6
    Join Date
    Jun 2017
    Location
    WI, USA
    Posts
    323
    Quote Originally Posted by wyboy View Post
    I have an optional standby generator servicing a structure. It is 1500 amps, 480/277. NEC 700.27, 701.27 (emergency systems and required standby) allow ground fault indication but Article 702 has no exception to the ground fault protection requirement for an optional standby generator so ground fault protection must be installed, correct?
    Correct. Additionally, you may want a second CT lead for the generator controller ground fault relay.