    I would go with the 2-5 wire splices jumpered together. Just use the correct wire nuts.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  2. #12
    Join Date
    Aug 2004
    Location
    Northern illinois
    Posts
    15,683
    Quote Originally Posted by bluecollar84 View Post
    I have a pvc box with 6-8 #12 ground thhn wires that I need to splice what's the best way to do this. Also this jbox is outdoors


    Sent from my iPhone using Tapatalk
    There are all kinds of options.

    Wire nuts and terminal strips are probably the simplest.

    Wire nuts are probably the fastest solution.

    https://www.automationdirect.com/adc...erminal_Blocks

    These are $2-3 each. I think you can get two wires on each side so you would only need two of them and a small piece of DIN rail to mount them on.
    Bob

  3. #13
    Join Date
    May 2011
    Posts
    3,808
    Are those WAGO connectors suitable for outdoor locations?

  4. #14
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,453
    Quote Originally Posted by jaggedben View Post
    Are those WAGO connectors suitable for outdoor locations?
    Actually, I never gave it a thought. Are wire nuts suitable for outdoor connections?
    Cheers and Stay Safe,

    Marky the Sparky

  5. #15
    Join Date
    Jan 2007
    Posts
    2,962
    Split bolt.

    JAP>

  6. #16
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,942
    Quote Originally Posted by jap View Post
    Split bolt.
    No good for 8-10 conductors although I've seen it done.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  7. #17
    Join Date
    Jan 2007
    Posts
    2,962
    Never really thought about it.


  8. #18
    Join Date
    May 2011
    Posts
    3,808
    Quote Originally Posted by K8MHZ View Post
    Actually, I never gave it a thought. Are wire nuts suitable for outdoor connections?
    I believe only those listed for it, such as DryConn.

    I don't think the WAGO are, just wondering if anyone can enlighten with specific info.

    Looking for something better than a Buchanan splice filled with Noalox, which isn't listed but which I personally trust a whole lot more than a wirenut with slippery goop inside.

  9. #19
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,749
    Quote Originally Posted by jaggedben View Post
    Are those WAGO connectors suitable for outdoor locations?
    Even twist on connectors probably have similar rating. I have been looking a little but found nothing yet on WAGO site, but wonder if one doesn't need to look in the UL white book.

    I would guess either is rated for use in wet/damp location enclosures, but not in submersible applications.

  10. #20
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,250
    Since the EGC does not have any current flow I can pre-twist them together and confidently use one of these.
    Attachment 17911