  1. #21
    Join Date
    Feb 2009
    Location
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,836
    Quote Originally Posted by edward View Post
    Since the EGC does not have any current flow I can pre-twist them together and confidently use one of these.
    Attachment 17911
    I don't know of any wire nut that is listed for more than five conductors.
    If Billy Idol or John Denver is on your play list go and reevaluate your life.

  2. #22
    Join Date
    Jun 2003
    Location
    NE (9.1 miles @5.07 Degrees from Winged Horses)
    Posts
    8,952
    A GBK14 is $8.50. It will take more time than that to get them under two twist ons.
    Tom
    TBLO

  3. #23
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,942
    Quote Originally Posted by edward View Post
    Since the EGC does not have any current flow I can pre-twist them together and confidently use one of these.
    Attachment 17911
    Quote Originally Posted by ActionDave View Post
    I don't know of any wire nut that is listed for more than five conductors.
    Those 3M Blue/Gray connectors are listed for up to 6-#10 AWG conductors.

    http://solutions.productos3m.es/3MCo...bute=ImageFile
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #24
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,749
    Quote Originally Posted by bluecollar84 View Post
    Is there an outdoor rated round bar that I can mount in a pvc enclosure ?


    Sent from my iPhone using Tapatalk
    It shoulnd't need to be mounted - doing so with a metal enclosure is a method of bonding to the enclosure. But I guess you still can mount it if you wanted.

  5. #25
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,942
    Is a ground bar required to be rated for damp/wet locations in an outdoor junction box?
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #26
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,250
    Quote Originally Posted by ActionDave View Post
    I don't know of any wire nut that is listed for more than five conductors.
    The specs say 6 #10 or #12.

    IMO, it will work especially if the wires are pretwisted.
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  7. #27
    Join Date
    Feb 2003
    Location
    Somewhere over the rainbow
    Posts
    3,250
    Quote Originally Posted by edward View Post
    The specs say 6 #10 or #12.

    IMO, it will work especially if the wires are pretwisted.
    I need to correct myself.

    The specs range is from 4 #14 to 6 #10. Not maximum 5#12s.

    If I have done this correctly:

    area of #10 is 10380 so 6 #10s = 62280 circular mils
    area of #12 is 6530 so 8 #12s = 52240 circular mils
    Edward
    The only thing I know, is the progressive discovery of my ignorance


  8. #28
    Join Date
    Jun 2015
    Location
    texas
    Posts
    1,575
    Quote Originally Posted by jaggedben View Post

    Looking for something better than a Buchanan splice filled with Noalox, which isn't listed but which I personally trust a whole lot more than a wirenut with slippery goop inside.


    Quote Originally Posted by ActionDave View Post
    I don't know of any wire nut that is listed for more than five conductors.
    The red bcaps top out at 5 #12's and the 2011 buchanan crimps can take up to 7 #12's- thought about mentioning those earlier but as Jaggedben pointed out, not 100% on the legality of the goop and the listing of those products....

    OTOH, depending on the circumstances, it may not even be necessary to use any type of sealant/anti cor. Lots of panels are outside, we don't do that to the joints in them, just plain old wirenuts, and no problems.

  9. #29
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,453
    Quote Originally Posted by user 100 View Post

    OTOH, depending on the circumstances, it may not even be necessary to use any type of sealant/anti cor. Lots of panels are outside, we don't do that to the joints in them, just plain old wirenuts, and no problems.
    Other than underground splicing, show me where it says that splices must be waterproof. Connectors, if used, don't even have to be listed, just identified for the use.
    Cheers and Stay Safe,

    Marky the Sparky

  10. #30
    Join Date
    Mar 2008
    Location
    Michigan. It's a beautiful penninsula, I've looked around.
    Posts
    9,453
    It would be legal to twist all 8 conductors together in a manner that provides all the mechanical integrity necessary for a good connection and then solder them. If the EGC's are bare, nothing more would be required, not even tape.
    Cheers and Stay Safe,

    Marky the Sparky