Page 2 of 2 FirstFirst 12
Results 11 to 15 of 15
Thread: 680.25(B) - Swimming Pool Panelboards
  1. #11
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,320
    Quote Originally Posted by infinity View Post
    Fundamentally I agree with you but the problem is to get to the requirement for a GES you have to have a structure. It would be better if it just stated all remote panels, even on a post, need a GES. If the panel was mounted to a tree no GES would be required. Doesn't make much sense.
    In this photo if one considers the two pieces of strut banged into the earth to be a structure then this is a violation because a single structure cannot have two branch circuits run to.
    Attachment 18033
    I get it but that is not what I was talking about. You don't have a panel so no electrodes are needed.
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  2. #12
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,364
    Quote Originally Posted by Dennis Alwon View Post
    But do you agree that you need the panel attached to a separate structure first to require the GES?
    Rob
  3. #13
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    33,320
    Imo, the panel must be attached to something- call it a structure or whatever- and therefore needs the electrode(s). A post is a structure. I may write a proposal that states if a panelboard is mounted remotely then it needs electrodes.
  4. #14
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,364
    That would end the confusion with whether or not it mounted to a structure when on a piece of strut or a post. Also that would include a panel mounted to a tree which does not meet the NEC definition of a structure.
    Rob
  5. #15
    Join Date
    Aug 2007
    Yachats Oregon
    Posts
    571
    Would this also apply to Recreational Vehicle Site Supply Equipment as described in 551.2 Definitions?
Posting Permissions
  • You may not post replies
  • You may not edit your posts