    if the incident level is 3.8 cal/cm2 after calculation. is HRC 2 is only required?

  2. #2
    Join Date
    Jul 2015
    Location
    Nebraska
    Posts
    59
    According to

    https://www.flameresistantuniforms.c...-rating-chart/

    HRC1 clothing would be sufficient. I think they are getting their info from NFPA 70E.

    Sent from my LGUS610 using Tapatalk

  3. #3
    Join Date
    Jun 2017
    Location
    WI, USA
    Posts
    154
    2015 NFPA 70E has clarified: hazard risk categories shall not be used with incident energy method (130.5(C)).

    If you were provided a calculated 3.8, see 70E Annex H: Table H.3(b)  Guidance on Selection of Arc-Rated Clothing and Other PPE for Use When Incident Energy Exposure Is Determined.

    Free NFPA access: http://www.nfpa.org/codes-and-standa...-and-standards