    Genreator Synchronzation

    Hello,
    In years past, when synchronizing generators a method called the one light out or 3 lights out has been taught to indicate synchronization. Would the same methodology hold true when using CFL's in stead of incandescent lamps? I cant find anything to specify one or the other. My thoughts lean toward NOT using CLF's for this test.

    Thanks,
    Xformer

  2. #2
    Join Date
    Feb 2003
    Location
    Seattle, WA
    Posts
    18,611
    The time delay involved in turning on a CFL would make it impractical, if not downright unsafe, to rely on them to indicate proper synchronization.
    Charles E. Beck, P.E., Seattle
    Comments based on 2014 NEC unless otherwise noted.

  3. #3
    Join Date
    Jul 2006
    Posts
    2,385
    I don't think LEDs would work either (dimmable, maybe?) since the whole procedure relies on the intensity of the lamps.

  4. #4
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    17,969
    Quote Originally Posted by zbang View Post
    I don't think LEDs would work either (dimmable, maybe?) since the whole procedure relies on the intensity of the lamps.
    Any lamp that goes out completely while a substantial voltage is still applied (e.g. LED ,or CFL, or even neon) will not be suitable for this use.