    Kern County and 705.12(D)

    I am stuck in a battle with Kern County (California) over their interpretation of 705.12(D), and am hoping that someone might have ideas on other ways to get them to agree with my interpretation. I am attempting to use this section to get out of the (D)(1) through (D)(7) requirements, specifically the 120% rule.

    Where distribution equipment, including switchgear, switchboards, or panelboards, is fed simultaneously by a primary source(s) of electricity and one or more utility-interactive inverters, and where this distribution equipment is capable of supplying multiple branch circuits or feeders, or both, the interconnecting provisions for the utility-interactive inverter(s) shall comply with 705.12(D)(1) through (D)(6).


    Our equipment is NOT capable of supplying multiple branch circuits, and not capable of feeding multiple feeders. Kern County's interpretation of this section is that 'multiple' does not apply to 'feeders' (only branch circuits). I have tried explaining that if this was the intent of the code, there would be an additional comma after 'multiple branch circuits'. They didn't like this.

    I have also tried arguing that if the definition of 'Feeder' is "circuit conductors between the service equipment... and the final branch-circuit overcurrent device.", then Feeders should mean multiple devices. They did not like this either. They gave the excuse that 'Feeder' is never used in the code (it is... 474 times. Feeders is used 239 times)

    I have contacted the California Building Standards Commission, who referred me to the Office of the State Fire Marshall. I am waiting for a call back right now, but even if I do get OSFM to agree with my interpretation, Kern County does not have to agree.


    Does anyone have any ideas of how I can get them to agree with my interpretation? Is my interpretation incorrect?

  2. #2
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    17,480
    A key question I have is whether there are loads connected to the distribution equipment.
    My interpretation for the "multiple" qualification" in the text is that multiple output OCPDs allow for the possibility of the sum of the current ratings being greater than the equipment rating even though there are two sources.
    If you have only one (or zero) output breaker, it is not possible to draw more than the device rating and the simple 100% rule would apply.

    Sent from my XT1585 using Tapatalk

  3. #3
    Join Date
    Oct 2013
    Location
    California
    Posts
    33
    Quote Originally Posted by GoldDigger View Post
    A key question I have is whether there are loads connected to the distribution equipment.
    My interpretation for the "multiple" qualification" in the text is that multiple output OCPDs allow for the possibility of the sum of the current ratings being greater than the equipment rating even though there are two sources.
    If you have only one (or zero) output breaker, it is not possible to draw more than the device rating and the simple 100% rule would apply.

    Sent from my XT1585 using Tapatalk

    There is one load connected to the distribution equipment (it is a large ag pump). A single line diagram would just be a straight line:
    Utility --> 800A service disconnect breaker --> 800A load breaker --> 800A load

    There is no busbar for distribution, and the main breaker feeds only the one load. This is why the interpretation of if 'feeders' is for multiple devices can mean the difference of the 120% rule or not.


    Also, a line side connection (tap) is not possible on this panel.

  4. #4
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    4,168
    Quote Originally Posted by anndee4444 View Post
    I am stuck in a battle with Kern County (California) over their interpretation of 705.12(D), and am hoping that someone might have ideas on other ways to get them to agree with my interpretation. I am attempting to use this section to get out of the (D)(1) through (D)(7) requirements, specifically the 120% rule.

    Where distribution equipment, including switchgear, switchboards, or panelboards, is fed simultaneously by a primary source(s) of electricity and one or more utility-interactive inverters, and where this distribution equipment is capable of supplying multiple branch circuits or feeders, or both, the interconnecting provisions for the utility-interactive inverter(s) shall comply with 705.12(D)(1) through (D)(6).


    Our equipment is NOT capable of supplying multiple branch circuits, and not capable of feeding multiple feeders. Kern County's interpretation of this section is that 'multiple' does not apply to 'feeders' (only branch circuits). I have tried explaining that if this was the intent of the code, there would be an additional comma after 'multiple branch circuits'. They didn't like this.

    I have also tried arguing that if the definition of 'Feeder' is "circuit conductors between the service equipment... and the final branch-circuit overcurrent device.", then Feeders should mean multiple devices. They did not like this either. They gave the excuse that 'Feeder' is never used in the code (it is... 474 times. Feeders is used 239 times)

    I have contacted the California Building Standards Commission, who referred me to the Office of the State Fire Marshall. I am waiting for a call back right now, but even if I do get OSFM to agree with my interpretation, Kern County does not have to agree.


    Does anyone have any ideas of how I can get them to agree with my interpretation? Is my interpretation incorrect?
    Move to NJ. The state can overrule the local AHJ. And they (the state) get cranky when local yokels start making up shirt pocket rules.

    Seriously, you seem to have fallen into a situation where invincible ignorance rules. Is there a local construction board of appeals you can go to, or would it be cheaper and easier to just comply?

  5. #5
    Join Date
    Dec 2012
    Location
    Placerville, CA, USA
    Posts
    17,480
    Complying might involve grossly oversized distribution equipment or, better if allowed, a supply side connection.

    Sent from my XT1585 using Tapatalk

  6. #6
    Join Date
    Apr 2007
    Location
    Berkeley, CA
    Posts
    1,264
    What does the equivalent section in the 2017 NEC have to say about what you'd like to do? If it is clearly allowed under the 2017 NEC, that might help convince the people you are dealing with that they are misinterpreting the 2014 NEC. Or perhaps they would give you permission to follow the 2017 NEC under section 90.4.

    Cheers, Wayne

  7. #7
    Join Date
    Oct 2013
    Location
    California
    Posts
    33
    Quote Originally Posted by wwhitney View Post
    What does the equivalent section in the 2017 NEC have to say about what you'd like to do? If it is clearly allowed under the 2017 NEC, that might help convince the people you are dealing with that they are misinterpreting the 2014 NEC. Or perhaps they would give you permission to follow the 2017 NEC under section 90.4.

    Cheers, Wayne
    The 2017 NEC is unchanged. I have already submitted comments for the 2020 NEC to be updated to clarify this issue.

  8. #8
    Join Date
    Oct 2009
    Location
    Austin, TX, USA
    Posts
    7,837
    Quote Originally Posted by anndee4444 View Post
    I am stuck in a battle with Kern County (California) over their interpretation of 705.12(D), and am hoping that someone might have ideas on other ways to get them to agree with my interpretation. I am attempting to use this section to get out of the (D)(1) through (D)(7) requirements, specifically the 120% rule.

    Where distribution equipment, including switchgear, switchboards, or panelboards, is fed simultaneously by a primary source(s) of electricity and one or more utility-interactive inverters, and where this distribution equipment is capable of supplying multiple branch circuits or feeders, or both, the interconnecting provisions for the utility-interactive inverter(s) shall comply with 705.12(D)(1) through (D)(6).


    Our equipment is NOT capable of supplying multiple branch circuits, and not capable of feeding multiple feeders. Kern County's interpretation of this section is that 'multiple' does not apply to 'feeders' (only branch circuits). I have tried explaining that if this was the intent of the code, there would be an additional comma after 'multiple branch circuits'. They didn't like this.

    I have also tried arguing that if the definition of 'Feeder' is "circuit conductors between the service equipment... and the final branch-circuit overcurrent device.", then Feeders should mean multiple devices. They did not like this either. They gave the excuse that 'Feeder' is never used in the code (it is... 474 times. Feeders is used 239 times)

    I have contacted the California Building Standards Commission, who referred me to the Office of the State Fire Marshall. I am waiting for a call back right now, but even if I do get OSFM to agree with my interpretation, Kern County does not have to agree.


    Does anyone have any ideas of how I can get them to agree with my interpretation? Is my interpretation incorrect?
    Under the 2014 NEC you can qualify a busbar for backfeeding if:
    a) 125% of the inverter nameplate current feeding your backfed breaker (anywhere on the bus) plus the OCPD protecting the busbar sum to 100% or less than the busbar rating.

    b) Your backfed breaker is located at the opposite end of the busbar from the OCPD protecting it, and 125% of the inverter nameplate current feeding it plus the OCPD protecting the busbar sum to 120% or less than the busbar rating (the 120% rule).

    c) All the breakers (load and backfed) connected to the busbar but disregarding the OCPD protecting the busbar sum to 100% or less than the rating of the busbar. This is the new one that legitimizes AC combiner panels that don't comply with the 120% rule.

    d) You run engineering studies backed up by a lot of data and you can get a PE to sign off on it.

    The rules are pretty clear and there is no other way AFAIK.

  9. #9
    Join Date
    Apr 2007
    Location
    Berkeley, CA
    Posts
    1,264
    Quote Originally Posted by ggunn View Post
    c) All the breakers (load and backfed) connected to the busbar but disregarding the OCPD protecting the busbar sum to 100% or less than the rating of the busbar. This is the new one that legitimizes AC combiner panels that don't comply with the 120% rule.
    I don't understand why 705.12(D)(2)(c) was written this way--wouldn't it be sufficient to either sum all the supply breakers, or sum all the load breakers, and if either sum is less than the ampacity rating of the busbar, then the busbar is adequately protected? If 705.12(D)(2)(c) were written that way, it would cover the OP's situation.

    As to the OP, I think if Kern County is going to misread 705.12(D) as you describe, you are stuck. I agree with your reading of 705.12(D), that if there can be only one load breaker in the equipment, 705.12(D)(1) through (6) do not apply.

    Cheers, Wayne

  10. #10
    Join Date
    May 2011
    Posts
    3,626
    Quote Originally Posted by anndee4444 View Post
    ...Our equipment is NOT capable of supplying multiple branch circuits, and not capable of feeding multiple feeders. Kern County's interpretation of this section is that 'multiple' does not apply to 'feeders' (only branch circuits). I have tried explaining that if this was the intent of the code, there would be an additional comma after 'multiple branch circuits'. They didn't like this.

    ...
    I'm trying to imagine what equipment you are dealing with where this description makes sense. If it's not capable of supplying multiple of either, then what difference does a comma make? In my experience, if you have a panelboard, then nearly by definition ("automatic overcurrent devices", plural) it is capable of feeding multiple branch circuits or feeders, or both. Unless this debate is about a circuit breaker enclosure or disconnect that is being incorrectly considered to be a panelboard, then my best guess is that I probably agree with the county's point of view about the rules that apply. But note that in the 2014 code the 120% rule (and the others ggunn described for you) only apply to panelboards, so if it isn't a panelboard, then that might be your last good bet at changing their minds. The other possibility might be if the busbars are on the supply side of the service disconnecting means, then the rules also don't apply.

    To be more succint, it's hard to help without knowing the details of the equipment and setup.
    Last edited by jaggedben; 07-13-17 at 11:24 PM.