    Can the grounded conductor of a cable assembly be reidentified as a grounded conductor?
  2. #2
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    32,856
    I assume you mean "Can a grounded conductor be re-identified as an ungrounded conductor and the answer is yes if it is part of a cable assembly
    They say I shot a man named Gray and took his wife to Italy
    She inherited a million bucks and when she died it came to me
    I can't help it if I'm lucky
  3. #3
    Join Date
    Dec 2006
    Chapel Hill, NC
    Posts
    32,856
    So did you come across a water heater cable that had the white conductor taped? Perfectly compliant.
  4. #4
    Join Date
    Jun 2015
    texas
    Posts
    1,697
    Quote Originally Posted by Electron plumber View Post
    As said above reidentifying a grounded (neutral- white) conductor into an ungrounded conductor is perfectly legal per the NEC-
    If you can get to a code book, (or maybe someone will post the passage in its entirety) its listed under 200.7(C)(1) in the 2014.
  5. #5
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,191
    Quote Originally Posted by user 100 View Post
    Here ya go:
    200.7 Use of Insulation of a White or Gray Color or
    with Three Continuous White or Gray Stripes.
    (A) General. The following shall be used only for the
    grounded circuit conductor, unless otherwise permitted in
    200.7(B) and (C):
    (1) A conductor with continuous white or gray covering
    (2) A conductor with three continuous white or gray stripes
    on other than green insulation
    (3) A marking of white or gray color at the termination
    (B) Circuits of Less Than 50 Volts. A conductor with
    white or gray color insulation or three continuous white
    stripes or having a marking of white or gray at the termination
    for circuits of less than 50 volts shall be required to
    be grounded only as required by 250.20(A).
    (C) Circuits of 50 Volts or More. The use of insulation
    that is white or gray or that has three continuous white or
    gray stripes for other than a grounded conductor for circuits
    of 50 volts or more shall be permitted only as in (1) and (2).
    (1) If part of a cable assembly that has the insulation permanently
    reidentified to indicate its use as an ungrounded
    conductor by marking tape, painting, or other
    effective means at its termination and at each location
    where the conductor is visible and accessible. Identification
    shall encircle the insulation and shall be a color
    other than white, gray, or green. If used for single-pole,
    3-way or 4-way switch loops, the reidentified conductor
    with white or gray insulation or three continuous
    white or gray stripes shall be used only for the supply
    to the switch, but not as a return conductor from the
    switch to the outlet.
    "Electricity is really just organized lightning." George Carlin
    Derek
  6. #6
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    35,680
    Quote Originally Posted by Dennis Alwon View Post
    I once had an inspector get out his marker and start coloring the white in a disconnect to a water heater, I then told him the water heater was a 120 volt unit.... He never really said anything and moved on.
  7. #7
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    7,777
    What is the proposal?
    Moderator-Washington State
    Ancora Imparo
  8. #8
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,071
    Quote Originally Posted by tom baker View Post
    Thanks - I'm shutting this down. The OP doesn't conform to this forum rules
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.
Posting Permissions
  • You may not post replies
  • You may not edit your posts