    Theoretical question:
    Taking away all aspects of listed equipment, Art 400, etc and looking at it from a grounding vs bonding question.
    If a heater is installed on a piece of equipment and fed by a 6 ft two conductor cord, and a bonding jumper is installed outside the cord jacket but attached to the cord per 250.102(E)(2), would the heater be considered to be sufficiently grounded ??
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  2. #2
    Join Date
    Jul 2015
    Location
    Wilmington, NC USA
    Posts
    272
    I would think it would be sufficiently bonded.

    Are you describing a cord and plug connection for power but a hard wired bond?

  3. #3
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,698
    I also agree on sufficiently bonded, as long as the bonding conductor has minimum size IAW 250.122.

  4. #4
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,442
    The ole bonded vs grounded... no doubt it's bonded... does that mean its acceptable by Code as "grounded" ?
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  5. #5
    Join Date
    Dec 2007
    Location
    NE Nebraska
    Posts
    33,698
    If whatever you bonded it to is grounded, yes.

    Art 100:

    Ground.
    The earth


    Grounded (Grounding).
    Connected (connecting) to ground or to a conductive body that extends the ground connection.

  6. #6
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,442
    In preparing my response to the person originally asking the question, I realized I was basing my answer on Code Sections that discuss raceway. In this particular situation we are using a cord. Does anyone know of a Code reference that specifically allows the equipment grounding conductor to be run outside of the jacket ?
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  7. #7
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    4,835
    Quote Originally Posted by augie47 View Post
    In preparing my response to the person originally asking the question, I realized I was basing my answer on Code Sections that discuss raceway. In this particular situation we are using a cord. Does anyone know of a Code reference that specifically allows the equipment grounding conductor to be run outside of the jacket ?
    Is there anything that forbids it? "Anything not forbidden is permitted."

  8. #8
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,442
    Quote Originally Posted by gadfly56 View Post
    Is there anything that forbids it? "Anything not forbidden is permitted."
    300.3(B) , as I read it, does not allow it.
    Last edited by jumper; 07-20-17 at 03:29 PM. Reason: fix NEC section
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  9. #9
    Join Date
    Jan 2009
    Location
    Maryland
    Posts
    12,296
    Quote Originally Posted by augie47 View Post
    300.3(B) , as I read it, does not allow it.
    Yep and I will through in 250.134(B) also.
    "Electricity is really just organized lightning." George Carlin


    Derek

  10. #10
    Join Date
    Oct 2007
    Location
    New Jersey
    Posts
    4,835
    Quote Originally Posted by augie47 View Post
    300.3(B) , as I read it, does not allow it.
    If it's an ungrounded receptacle, could 250.130(C) apply?