Page 3 of 3 FirstFirst 123
Results 21 to 22 of 22
Thread: Cable Seals 501.15(E)
  1. #21
    Join Date
    Apr 2004
    Mission Viejo, CA
    Posts
    5,191
    Quote Originally Posted by rbalex View Post
    So make a Public Input. You're running out of time though.
    I'm yanking your chain again although it's still a good idea to learn how to make a Public Input.
    Technically, stranded conductors are cables and solid conductors are not. See Webster’s Collegiate Dictionary, 11th edition definition of cable. (Definition 1 as opposed to 3). Webster’s Collegiate Dictionary, 11th edition, is NFPA's "official" dictionary when words are not defined within the context of an NFPA standard or standards. Fortunately, Merriam-Webster's online edition uses identical definitions.
    You might suggest that the first sentence of Subsection 501.15(D)(1) be revised to read, "Multiconductor cables shall be sealed with sealing fittings that comply with 501.15(C) at all terminations."
    "Bob"
    Robert B. Alexander, P.E.
    Answers based on 2014 NEC unless otherwise noted.
  2. #22
    Join Date
    Apr 2016
    Georgia
    Posts
    490
    Thanks again Bob, as always great input.