    Electrode grounding conductor lugs that are listed for use to building steel

    I am looking for some assistance on finding which type of lugs are listed for use to install the electrode grounding conductor to building steel.
    Any help would be appreciated.

  2. #2
    Join Date
    Feb 2009
    Location
    NY
    Posts
    1,541

  3. #3
    Join Date
    Jul 2005
    Location
    Tennessee
    Posts
    15,388
    Unless there is something unusual about your application, most all crimp, mechanical and cadweld type lugs are so listed. Check your manufacturers catalog.

    http://www.burndy.com/docs/default-s...t.pdf?sfvrsn=0
    At my age, I'm accustomed to restaurants asking me to pay in advance, but now my bank has started sending me their calendar one month at a time.

  4. #4
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,569
    Are you drilling the steel to attach the lug with a bolt? If so then you can use just about any lug. If you're looking for a clamp type connection without drilling then you can purchase one of those listed for the purpose.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted