    What happened here?

    Attached are pictures of an overload unit that got hot. At first glance it would appear to be a loose connection on the B phase and as it loosened up it got warm. This runs a 40 HP pump. It was installed last summer and is used for the cooling of the building, so it didn't even run that much as we are in Wisconsin, and we don't cool that much in the winter. If you look closely you can still see a piece of the #6 AWG wire in the lug. The copper wire actually got so hot that it appears to have melted (separated just outside of the lug). The interesting thing is that 6 inches down the conductor from this point, the insulation was still flexible. The overload, I'm told never tripped and was never reset. So in my mind the wire got really hot, enough to melt the copper into to pieces, but not stay hot long enough to transfer any heat to further down the conductor. Any thoughts what would cause all of this? Someone mentioned lightning, which kind of makes sense as this combination starter is the shortest run from our 3000 amp service. But this was the only damage. If it were lightning, I would expect to see the lightning finding a path to ground somewhere. Any thoughts are appreciated.
    Attached Thumbnails Attached Thumbnails Click image for larger version. 

Name:	IMG_0582.jpg 
Views:	387 
Size:	134.2 KB 
ID:	18109   Click image for larger version. 

Name:	IMG_0583.jpg 
Views:	326 
Size:	131.2 KB 
ID:	18110   Click image for larger version. 

Name:	IMG_0585.jpg 
Views:	317 
Size:	126.1 KB 
ID:	18111   Click image for larger version. 

Name:	IMG_0587.jpg 
Views:	297 
Size:	150.5 KB 
ID:	18112   Click image for larger version. 

Name:	IMG_0588.jpg 
Views:	299 
Size:	124.2 KB 
ID:	18113  

    Click image for larger version. 

Name:	IMG_0589.jpg 
Views:	285 
Size:	131.3 KB 
ID:	18114  

  2. #2
    Join Date
    Apr 2007
    Location
    Huntington Beach, CA (19 Hrs. 22 Min. from Winged Horses)
    Posts
    6,198
    Quote Originally Posted by rhamblin View Post
    Attached are pictures of an overload unit that got hot. At first glance it would appear to be a loose connection on the B phase and as it loosened up it got warm. This runs a 40 HP pump. It was installed last summer and is used for the cooling of the building, so it didn't even run that much as we are in Wisconsin, and we don't cool that much in the winter. If you look closely you can still see a piece of the #6 AWG wire in the lug. The copper wire actually got so hot that it appears to have melted (separated just outside of the lug). The interesting thing is that 6 inches down the conductor from this point, the insulation was still flexible. The overload, I'm told never tripped and was never reset. So in my mind the wire got really hot, enough to melt the copper into to pieces, but not stay hot long enough to transfer any heat to further down the conductor. Any thoughts what would cause all of this? Someone mentioned lightning, which kind of makes sense as this combination starter is the shortest run from our 3000 amp service. But this was the only damage. If it were lightning, I would expect to see the lightning finding a path to ground somewhere. Any thoughts are appreciated.
    i'm guessing here, but i'd call it an internal failure of the overload, not from an external factor.

    probably failed when the hole melted and let out the magic smoke.
    magic smoke is a lot like SF6 gas on HV breakers.
    ~New signature under construction.~
    ~~~~Please excuse the mess.~~~~

  3. #3
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,922
    Looks like the stab that connects to the bus was loose. I've seen them with the attachment bolt loose straight from the factory.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  4. #4
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    7,005
    That appears top be an A-B E1 solid state overload relay, so it would not directly sense the heat of a bad connection as a bi-metal one would. A loose connection then would concentrate the heat of the added resistance right at the terminal, then if mounted vertically, the heat would rise INTO the rest of the OL relay and the tang that is connecting it to the contactor. Heat doesn't tend to migrate downward very much.

    What kind of wire was this by the way? Mechanical lugs like this are not rated for high strand count conductors. I have seen this issue many times as a result of people not understanding this and using extra flexible cable because it's easier to work with.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  5. #5
    Join Date
    Jul 2003
    Location
    New Jersey
    Posts
    23,922
    I think that the first guess would be a loose connection. Figuring out where it was loose is the hard part.
    Rob

    Moderator

    All responses based on the 2014 NEC unless otherwise noted

  6. #6
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    7,005
    Quote Originally Posted by infinity View Post
    I think that the first guess would be a loose connection. Figuring out where it was loose is the hard part.
    Agreed. But I worked for a number of years with a PE that did forensic investigations of electrical equipment failures and accidents. One thing I picked up from him is that you can usually tell where something started by looking at the damage path from worst to least, and the source will almost always be the worst, but following the rule that heat rises. So in this case the wire lug is the worst and was likely at the bottom, the tang for the contactor was likely at the top and shows less damage, so it was likely collateral to the bad wire connection.
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  7. #7
    Join Date
    Feb 2009
    Location
    Kaukauna, Wisconsin
    Posts
    73
    Thanks for all the reply's guys. It was mounted vertically, and had THHN wire under the lugs. And it was an Allen Bradley E1 Plus.


    Sent from my iPhone using Tapatalk

  8. #8
    Join Date
    Jun 2003
    Posts
    6,748
    Quote Originally Posted by Jraef View Post
    Agreed. But I worked for a number of years with a PE that did forensic investigations of electrical equipment failures and accidents. One thing I picked up from him is that you can usually tell where something started by looking at the damage path from worst to least, and the source will almost always be the worst, but following the rule that heat rises. So in this case the wire lug is the worst and was likely at the bottom, the tang for the contactor was likely at the top and shows less damage, so it was likely collateral to the bad wire connection.
    Quote Originally Posted by rhamblin View Post
    Thanks for all the reply's guys. It was mounted vertically, and had THHN wire under the lugs. And it was an Allen Bradley E1 Plus.


    Sent from my iPhone using Tapatalk
    So with it being regular THHN wire, I'm going to guess maybe the wire lug was never tightened properly?

  9. #9
    Join Date
    Jul 2006
    Location
    San Francisco, CA, USA
    Posts
    7,005
    Quote Originally Posted by rhamblin View Post
    Thanks for all the reply's guys. It was mounted vertically, and had THHN wire under the lugs. And it was an Allen Bradley E1 Plus.


    Sent from my iPhone using Tapatalk
    Thanks for the update.
    THHN should have been fine, so it was most likely just not tight enough. That size unit needs 40 lb-in of torque.

    My guess:
    Cell phone rang right when the installer was supposed to be paying attention...
    __________________________________________________ ____________________________
    Many people are shocked when they discover I am not a good electrician...

  10. #10
    Join Date
    Apr 2009
    Location
    Williamsburg, VA
    Posts
    4,244
    Loose connection was my first guess.