Results 1 to 7 of 7
Thread: Ufer in a Metal Building
  1. #1
    Join Date
    Apr 2008
    Posts
    2
    New addition to existing building. The addition is 40,000 feet. The fountation has the approiate rebar stub from the foundation footing. The question that has come up is now the 15 interior collums in the center of the building. They are individual 10'x10'x2' chunks of concrete with rebar in them. Do each of these need to be grounded too?
  2. #2
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,201
    You only need one GEC to the foundation rebar. The rest of the steel columns should be bonded by the interlocking building steel, often the roof trusses and steel header beams between columns.
    "Electricity is really just organized lightning." George Carlin
    Derek
  3. #3
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,364
    Even if the structure is built so that it has multiple CEE's you only need to use one.
    Rob
  4. #4
    Join Date
    Aug 2004
    Northern illinois
    Posts
    16,801
    Quote Originally Posted by infinity View Post
    and if there is one in the existing part of the structure you don't have to do anything as far as CEE goes.
    Bob
  5. #5
    Join Date
    Jun 2006
    Ohio
    Posts
    21,385
    The structural metal needs bonded 250.104(C), but just going by what you describe, the columns are not grounding electrodes 250.52(A)(2).
    I will have achieved my life's goal if I die with a smile on my face.
  6. #6
    Join Date
    Apr 2008
    Posts
    2
    Quote Originally Posted by petersonra View Post
    That's exactly what we have multiple CEE but where does it say I only need to use one. I am being told I have to use them all
    Sent from my SM-G920V using Tapatalk
  7. #7
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,364
    Not required by the NEC:
    250.52(A)(3) Concrete-Encased Electrode. A concrete-encased elec-trode shall consist of at least 6.0 m (20 ft) of either (1) or (2):
    (1) One or more bare or zinc galvanized or other electri-
    cally conductive coated steel reinforcing bars or rods of
    not less than 13 mm ( 1 ⁄ 2 in.) in diameter, installed in
    one continuous 6.0 m (20 ft) length, or if in multiple
    pieces connected together by the usual steel tie wires,
    exothermic welding, welding, or other effective means
    to create a 6.0 m (20 ft) or greater length; or
    (2) Bare copper conductor not smaller than 4 AWG
    Metallic components shall be encased by at least 50 mm
    (2 in.) of concrete and shall be located horizontally within that
    portion of a concrete foundation or footing that is in direct
    contact with the earth or within vertical foundations or struc-
    tural components or members that are in direct contact with
    the earth. If multiple concrete-encased electrodes are present
    at a building or structure, it shall be permissible to bond only
    one into the grounding electrode system.
    Rob