    I'm trying to size branch circuit OCPD and conductors for an elevator motor. The only data that I have for the motor is 16 HP at 30.6 RPM, and the utility voltage 208/3 phase.
    For sizing the OCPD I need motor HP so my first thought what exactly is this info "16 HP at 30.6 RPM" even used for?
    How do I get the HP to use for sizing the OCPD?
    Does 30.6 RPM suggest a multi speed or low speed motor?
  2. #2
    Join Date
    Apr 2009
    Williamsburg, VA
    Posts
    5,438
    Quote Originally Posted by cppoly View Post
    There's nothing from the mfg of the motor, drive unit, hydraulics unit, elevator mfg?
    30.6RPM seems to indicate to me a DC motor, reduction gearbox or most likely a VFD to achieve such a low, precise number, tho I admit I know about as much as elevator motors as I do biological invisibility cloaks for polka-dotted unicorns. A Google search of "16 HP at 30.6 RPM" yielding one result with that exact phrase: this thread.
    istm to be too easy to simply size the conductors and OCPD for a 16HP motor, keeping voltage drop at a low (3% or less) amount.
  3. #3
    Join Date
    Apr 2012
    New York
    Posts
    558
    Thanks. I will look further into it from the manufacturer.
    But, what are you supposed to do when you are given a HP that doesn't match up with the HP in the NEC tables? Just round UP? 16 --> 20 HP?
  4. #4
    Join Date
    Dec 2010
    Posts
    1,389
    I wouldn't round up. Maybe use the nameplate information?