Page 11 of 13 FirstFirst ... 910111213 LastLast
Results 101 to 110 of 129
Thread: Can someone please explain this to me?
  1. #101
    Join Date
    Feb 2003
    Post Falls, ID
    Posts
    74
    Quote Originally Posted by jrohe View Post
    I suspect they are expecting you to use the method that uses DC-constant resistance for determining voltage drop to calculate the minimum wire area, in cmils, required.
    For single phase circuits (assumed because that information is missing in the test in the question), the equation is:
    VD = 2 x K x I x D / CM
    Rearranging the equation to solve for CM results in the equation:
    CM = 2 x K x I x D / VD
    Making assumptions for copper conductors and VD% cannot exceed 3 percent because the information is missing in the test question:
    K = 12.9 ohms
    I = 30 amps
    D = 100 feet
    VD = 230 volts x 0.3 = 6.9 volts
    Therefore:
    CM = 2 x 12.9 x 30 x 100 / 6.9 = 11217.4 cmils.
    Looking at Chapter 9, Table 8, the smallest conductor with this area is #8 AWG conductor at 16510 cmils. A #10 conductor has an area of 10380 cmils, which is too small, at least according to this calculation method.
    I agree completely with this reply by Jason; he is spot-on correct.
  2. #102
    Join Date
    Jun 2003
    Posts
    6,801
    Quote Originally Posted by steve66 View Post
    Actually, I think the Southwire calculator assumes 3 phase. That makes a bigger difference than the power factor. I don't seen anywhere on the Southwire calculator where I can choose 1 phase.
    But back to the power factor - it makes some difference in the calculated impedance of the wire. If you know R and X for a wire, then Z depends on R and X and the power factor.
    Z = X*PF+R*Sin(Acos(PF))
    (I think that's right - I'm trying to read it from an excel formula.)
    Just as an example, my Square D calculator lists L-L voltage drop per amp per 100' in magnetic copper wire: (trying to make a table, which isn't working)
    ....................... ..... #8 Wire #10 wire
    1 phase: 90% PF. . 0 .15 ....... . 0 .23
    1 phase: 80% PF ...0.13 ........ 0 .20
    3 phase: 90% PF .. 0 .13 ........ 0 .20
    3 phase: 80% PF... 0 .11 ........ 0 .17
    Quote Originally Posted by oldsparky52 View Post
    So, ... as PF goes farther away from 1, the resistance in the circuit becomes less? So the worse the PF the less resistance?
    Not quite. First of all, we are talking about the wire impedance, not just resistance.
    And a low PF makes the voltage drop a little less for small wire where the wires resistance is fairly large compared to the wires reactance.
    But for larger wires, where reactance is larger, the voltage drop is less for higher power factors, with 2/0 wire actually having about the same drop for 95% PF and 80% PF.
  3. #103
    Join Date
    Jan 2009
    Maryland
    Posts
    13,086
    Quote Originally Posted by Ingenieur View Post
    perhaps
    but he is correct
    Agree with both.
    "Electricity is really just organized lightning." George Carlin
    Derek
  4. #104
    Join Date
    Feb 2009
    Durango, CO, 10 h 20 min without traffic from winged horses.
    Posts
    8,987
    Quote Originally Posted by jumper View Post
    Agree with both.
    Don't push me.
    If Billy Idol or John Denver is on your play list go and reevaluate your life.
  5. #105
    Join Date
    Jan 2016
    PA
    Posts
    4,500
    Agree with both.
    Without being too snarky not sure how he could disagree lol
  6. #106
    Join Date
    Aug 2017
    Orange tx
    Posts
    8
    8 awg is correct!
    Mike uses the formula 2xKxIxD/Vd to find the circular mils of the wire.
    nec recommends no more the 3% so..
    vd=6.9 voltage drop (3%of 230)
    D=100' distance
    I=30a current
    K=12.9 for copper wire.
    cmils= 2x12.9x30x100/6.9 = 11,217cmils
    Chapter 9 table 8 back of book
    10awg = 10380 =too small to limit vd to 3%
    8awg = 16510= correct
  7. #107
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    34,253
    Quote Originally Posted by Daniel malack View Post
    I just looked on several breakers GE 40°, Sq D home line 40°, Sq D QO 40°, Siemens 40°, Cutler Hammer Ch 60-75° Cutler Hammer bolt in 60-75° most are 40°. I got no reason to lie to ya.
    Sent from my SM-T350 using Tapatalk
    40 deg rating is not terminal temp rating it is the ambient temp that the trip rating was calibrated for.
  8. #108
    Join Date
    Nov 2015
    Plano, TX USA
    Posts
    25
    Branch Circuit VD is 3%
    VD= 2KIL/CM
    (2 X 12.9 X 30 X 100) / 16510 = 4.68 Volts
    230 X .03 = 6.9 volts allowed
    B is correct
    #10 would allow 7.45 volts
  9. #109
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    8,686
    For balanced loads another way to look at is is Vd = IR in a single conductor one way regardless of service type (single or three phase) and then multiply by the line to phase voltage ratio (2 or sqrt3).
  10. #110
    Join Date
    Jul 2015
    Wilmington, NC USA
    Posts
    281
    Quote Originally Posted by ggunn View Post
    That's all I do for sizing a wire to a known load. Any more complicated and an EE does it.