Thread: 210.52(C)(3)
  1. #1
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,993
    210.52(C)(3)
    Which rendition is correct?
    NEC 2017 210.52 (C) Countertops and Work Surfaces.(3) Peninsular Countertop Spaces. At least one receptacle outlet shall be installed at each peninsular countertop long dimension space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater. A peninsular countertop is measured from the connected perpendicular wall.
    Attached Thumbnails Attached Thumbnails Click image for larger version.
Name:	210.52 C 3 layout A.jpg
ID:	18166   Click image for larger version.
Name:	210.52 C 3 layout B.jpg
    CircuitRyder --- Unfortunately not all good ideas are code enforceable.
  2. #2
    Join Date
    Jan 2009
    3 Hr 2 Min from Winged Horses
    Posts
    14,201
    We had a thread on this last year. I never actually figured out exactly what they want in the 2017.
    Since I do not wire resi kitchens, I gave up trying to understand. Maybe this thread will give a simpler answer.
    http://forums.mikeholt.com/showthread.php?t=180259
    "Electricity is really just organized lightning." George Carlin
    Derek
  3. #3
    Join Date
    Apr 2003
    Fort Collins, Colorado
    Posts
    1,666
    Based on the thread Jumper provided, I vote the drawing on the left is approved by the 2017 NEC.
    JMHO
    Ron
  4. #4
    Join Date
    Feb 2003
    Bremerton, Washington
    Posts
    7,872
    In Washington we stayed with the 2014 language.
    Moderator-Washington State
    Ancora Imparo
  5. #5
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,993
    Quote Originally Posted by rcarroll View Post
    JMHO
    I would agree the wording is describing the left drawing but it is interesting that the NEC commentary uses the right side drawing for an example. Puts inspectors in a controversial setting.
  6. #6
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,993
    Quote Originally Posted by tom baker View Post
    would that be the rightside or leftside drawing? very political answer
  7. #7
    Join Date
    Feb 2013
    Aspen, Colo
    Posts
    1,993
    Quote Originally Posted by jumper View Post
    Not really -- LOL
  8. #8
    Join Date
    Jan 2009
    Posts
    14,201
    Quote Originally Posted by mwm1752 View Post
    The 2017 NECHB commentary?
    Derek
  9. #9
    Join Date
    Apr 2003
    Posts
    1,666
    Yes.
    Ron
  10. #10
    Join Date
    Mar 2014
    Utopia
    Posts
    1,367
    Your layout A is correct. (0ne on the left) However, nothing would prohibit your enhanced layout B as well...more is better in this case and look for a change to clarify things a bit in the 2020 cycle.