    Just passed md contractors exam & couple of questions are still stumping me:
    1.What % of secondary current is protected by primary ocpd?(I forget trx setup or %s)
    2. Whats minimum times current is a fuse allowed to protect >600v service? Smallest choice was 1.
    3. What is voltage to ground for b phase on 240v ungrounded(?) delta? I chose 208, but what's reference ground, primary ground?
    ty
  2. #2
    Join Date
    Jul 2017
    Glen Rock, Pa
    Posts
    10
    4. What's smallest size conductor allowed in parallel? I chose 1/0, but couldn't also be 6awg for gec?
    Sent from my SAMSUNG-SM-G891A using Tapatalk
  3. #3
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,745
    Quote Originally Posted by gunpowder View Post
    ty
    1. Not sure the actual question here, but thinking you are looking for primary to secondary ratio to be involved here?
    2.
    3. If it is an ungrounded system the voltage to ground can be fairly unpredictible as there is no ground reference until there is a ground fault on something.
    4. 1/0 is the correct general rule answer. You can't parallel GEC's or EGC's for the purpose of effectively making a larger capacity conductor out of smaller conductors. You still end up with parallel paths in many instances though.
  4. #4
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,180
    1) Look at 450.3
    2) Not sure the way the question is written.
    3) Ungrounded=0
    4) Forget GEC's, #1/0 look at 310.10(H).
    Rob
  5. #5
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,745
    Quote Originally Posted by infinity View Post
    1) Look at 450.3
    3) Ungrounded=0
    Your #3 answer vs my #3 answer is all about capacitive effects, otherwise the theoretical answer is 0, if there are no ground faults in the system.
  6. #6
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,428
    Quote Originally Posted by kwired View Post
    I would say the answer is "undefined". If you put a meter from the B phase to ground, you probably won't see 0V, but rather some nonsense number. If "none of the above" is a choice, then it's the right one no matter what the other choices are, IMO.
  7. #7
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,745
    Quote Originally Posted by ggunn View Post
    I agree.
  8. #8
    Join Date
    Oct 2009
    Austin, TX, USA
    Posts
    9,428
    I agree.
    Some test questions are designed to make you burn up test time trying to do calculations if you do not understand the underlying principle that makes the calculations unnecessary or futile. Sneaky.
    In a multiple choice test the first thing you should do on every question is to see which of the answers you can rule out without doing much if any calculation.
  9. #9
    Join Date
    Dec 2007
    NE Nebraska
    Posts
    36,745
    Also agree.
  10. #10
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,180
    I would guess that the answer undefined wasn't on the test so you would need to look for the theoretical answer which should be 0 since it says that it's ungrounded.
    Rob