    compliance with 700.10(D)(1)
    In situations such as this where sprinklers are used to comply with 700.10(D)(1) I wonder what constitutes sprinkler protection. The reason I ask is that in most situations the space where the feeder is running, say, above a suspended ceiling is not sprinklered-only the space below. Does this meet the requirement of 700.10(D)(1)(1)?
    We have a similar job as this and are not sure of the answer. There seems to be argument both ways on this.
  4. #14
    Join Date
    Oct 2007
    New Jersey
    Posts
    5,833
    Quote Originally Posted by texie View Post
    You would have to go to NFPA 13 to decipher what "fully sprinklered" would mean in any given situation. If the area above a suspended ceiling is for "other envrionmental air" (plenum) but otherwise is non-combustible, you don't need sprinklers in the cavity. If the T.O.C. is wood joists and decking, now you need it. You wouldn't put sprinklers in the wall cavities, for instance. The sprinklers are designed to keep the fire away from the cable, not pour water on the cable directly.
  5. #15
    Join Date
    Jul 2003
    New Jersey
    Posts
    25,355
    If you can figure out what class of building and occupancy he has from his OP, you are WAY better at this than I am.
    I narrowed it down to just about any building in NYC that has MI cable would have sprinklers.
    Rob
  6. #16
    Join Date
    Nov 2010
    Posts
    2,638
    Yes, I see your logic and think I agree. In other words, if the building meets the requirements as a fully sprinklered building, then it is "fully protected by an approved automatic fire suppression system" per the NEC. I think your wall cavity example makes the point well-you wouldn't put sprinklers in a wall cavity just because it had an Art. 700 feeder it. The same would be true for the unsprinklered space in a ceiling as that may be no different than a wall cavity in many situations.
Posting Permissions
  • You may not post replies
  • You may not edit your posts